@chris301up you may understand the need for isolation, but do you have the knowledge and tools to practice safe isolation?

The existing 6mm cable is already 20m long, have you referenced BS7671 to check suitability of the new extended length in 6mm, taking account of installation method, rating factors, voltage drop, and maximum earth fault loop impedance to meet required CPD disconnection times, for the design current?

Please call a sparky in before you hurt yourself, or someone else.
 
FAQs - IET Electrical - https://electrical.----------/bs-7671/building-regulations/part-p-england-and-wales/faqs/

This might clear a few things up for you sir
 
Last edited by a moderator:
I understand the supply must be isolated at supply, and yes, a RCD is a sensitive safety device that switches off electricity automatically if there is a fault, and designed to protect against the risks of electrocution and fire caused by earth faults.

All I was confused about is why the RCD should trip when nothing is connected to that circuit, except the new short length of cable and a junction box.

In other words no, you don't understand how an RCD works, just a rough idea of the protection it provides.
An RCD trips when there is an imbalance between the current flowing through the circuit conductors, generally this is as a result of current flowing to earth, this can be directly from L to E or by neutral current being diverted via a N to E fault.

So an RCD will trip with nothing connected to the circuit if there is a low resistance from N to E.
Can you confirm exactly what you have done to isolate this circuit? If you have not isolated both L and N then it is easy for the open end of the cable to present a N to E fault an dtrip the RCD.
 
........It worked before. You touched it. It now doesn't work and you don't know why.....

My point exactly. All I have done is added a 60amp junction box with a short 6mm cable extension, which isn't connected to anything.
 
My point exactly. All I have done is added a 60amp junction box with a short 6mm cable extension, which isn't connected to anything.

The fact that when you disconnect this, the fault is gone, points to you either installing a damaged cable, or incorrectly.

I presume as you are DIY you have nothing available to test with?
 
Yes I am DIY. I am just going to have another look at this shortly. Have a multi-meter if that helps?

Could the junction box be faulty is also a question at the back of my mind?
 
Okay everyone. Have had another look at the problem this morning and can confirm that it looks like the junction box is the cause. When connecting just the junction box to the existing wiring the RCD trips. No extension cable attached at this stage.

Just a bit of trial and error! I connected a standard 30amp junction box, together with the new extension cable, and all is well. RCD not tripping. Nothing else connected to the cable. I'll order another junction box and go from there. Thanks everyone for your kind advice
 
Well if you have no idea what you are doing and have no way to test if it will be safe then I suppose trial and error is your only way to diagnose a fault. Not that you have done that for sure.
Don't forget to cross your fingers when energising to replace basic test procedure.
 
Yes I am DIY. I am just going to have another look at this shortly. Have a multi-meter if that helps?
Unlikely... in fact probably unhelpful in that if you don't know what you are doing, you could end up hurting yourself. Read this thread. If you value yours and your family's lives and your home, you will call an electrician.
 