I have not noticed RCBOs are warm all of the time, and i am often using large distribution units with over 100 rcbos in and for some shows half of then wont be used, i would say those are at room tempWylex specs says full load losses are 1.5 to 2.6 watts per pole. DP is twice the load of SP. You must have noticed RCBOs are warm all the time, even when there is no load running through them. This also makes the insides of a metal CU case warmer. I assume the 1.5 watts is no load energy consumption,