Sooby2

-
Reaction score
38
I've just started at a new church and the electrics are bit of a shambles. I'm not going to be touching them as I'm not qualified, but one thing I have been told is this, which I'm not sure is correct (and really doesn't sound right).

Sometime in the 90's the building was rewired by SEEBoard, who used twin core cable, the earth system being provided by the conduit which uses slip couplings. This failed in fairly short order and left many circuits with no earth - there's a very lengthy associated story of trying to get it rectified and failing.

To repair this now would mean ripping everything out and starting again, which they're keen to avoid. Apparently a few years ago an electrician stated it is fine to keep using these circuits, complete with metal faced switches and sockets, along with sockets now having no earthing system, as he fitted RCBO's to the circuit as and I quote "these are suitable for circuits without an earth arrangement".

Is that right? I've only done the EAL Level 3 and don't call myself an electrician, but this doesn't sound right to me? I'm aware of Regulation 411.3.1.1 & BS7671 which is why I'm struggling to believe this is correct. However I'm very happy to be put right if that is the case. Thanks.
 
No, the use of an RCD/RCBO does not mitigate the omission of a CPC for the circuit. No earth and metal sockets in use sounds like an accident waiting to happen.

I'm surprised that an electrician said they were safe for continued use.

Maybe have an extra little prayer this Sunday!
 
Last edited:
This is intriguing for a few reasons as a lot doesn't really make too much sense at face value.
How exactly has the conduit installation failed? There's nothing wrong with slip-couplings if installed properly. A photo would probably be worth 1000 words!
I'm also surprised it's a big deal to fix. The regs allow a suitably sized earth to be shared by final circuits and I'd have imagined there would be a last-resort option of earthing the conduit further along.

Guessing a bit, it sounds as though the church needs to find the right sparks for the job. It isn't the right sort of thing for a mainly domestic sparks as a fair few of them would baulk at anything unusual and run a mile from galv conduit. That isn't to say that there aren't good all-rounders out there who do domestic work though!

From the time scales you mention I'd imagine that the installation is now overdue an EICR and hopefully this will provide a chance to put right this dangerous situation.
 
This is intriguing for a few reasons as a lot doesn't really make too much sense at face value.
How exactly has the conduit installation failed? There's nothing wrong with slip-couplings if installed properly. A photo would probably be worth 1000 words!
I'm also surprised it's a big deal to fix. The regs allow a suitably sized earth to be shared by final circuits and I'd have imagined there would be a last-resort option of earthing the conduit further along.

Guessing a bit, it sounds as though the church needs to find the right sparks for the job. It isn't the right sort of thing for a mainly domestic sparks as a fair few of them would baulk at anything unusual and run a mile from galv conduit. That isn't to say that there aren't good all-rounders out there who do domestic work though!

From the time scales you mention I'd imagine that the installation is now overdue an EICR and hopefully this will provide a chance to put right this dangerous situation.

We had a building team meeting this afternoon and I was able to get more detail. I could send you a photo of a wall with the conduit buried in it, although I'm not sure that would help! . The problem of the conduit being buried in the walls means we don't know where the joints are that have failed, but apparently there is no earth continuity along them. We're looking at running an earth to each socket (or line of sockets if there is continuity between them). We do have a proper electrical contractor now who is competent with commercial and he has done a proper job on the most recent parts of the building.

We are due another EICR next year and they're just working through the known issues. Like all old, extended buildings we have a mashup of systems. Back in the 90's SeeBoard rewired original building and made a complete mess of it, which is where "if installed correctly" falls down. Apparently it was so bad SeeBoard were reported to their trade body at the time.

It seems possible that somehow RCBO's were installed on those circuits affected, although no-one can remember when - and since then they've been missed out of testing as only a percentage of circuits were tested each time by different contractors (and we have a lot, it's a big building now). I've advised we get our current contractor in tomorrow and check the affected circuits to see if they are safe and compliant and I'm told is going to happen.
 
We had a building team meeting this afternoon and I was able to get more detail. I could send you a photo of a wall with the conduit buried in it, although I'm not sure that would help! . The problem of the conduit being buried in the walls means we don't know where the joints are that have failed, but apparently there is no earth continuity along them. We're looking at running an earth to each socket (or line of sockets if there is continuity between them). We do have a proper electrical contractor now who is competent with commercial and he has done a proper job on the most recent parts of the building.

We are due another EICR next year and they're just working through the known issues. Like all old, extended buildings we have a mashup of systems. Back in the 90's SeeBoard rewired original building and made a complete mess of it, which is where "if installed correctly" falls down. Apparently it was so bad SeeBoard were reported to their trade body at the time.

It seems possible that somehow RCBO's were installed on those circuits affected, although no-one can remember when - and since then they've been missed out of testing as only a percentage of circuits were tested each time by different contractors (and we have a lot, it's a big building now). I've advised we get our current contractor in tomorrow and check the affected circuits to see if they are safe and compliant and I'm told is going to happen.

Needs a full EICR now by the sounds of it, not next year. Be interesting to see what else is found.

Is there space in the conduits for new earths to be run inside them?
 
Needs a full EICR now by the sounds of it, not next year. Be interesting to see what else is found.

Is there space in the conduits for new earths to be run inside them?
True, although it's scheduled for January. I did ask if there was room or could we repull the cables with T&E but apparently the conduits are full and it's not an option. How that works for heat dissipation is another question.
 
@Sooby2 thanks for explaining more. It sounds like things are moving in the right direction, but I'd agree that an EICR is needed asap.
The recent kids pub car park death through lack of earthing should help focus minds if minds need focussing, and I'd be advising socket circuits are locked off until this is rectified.

As you say, finding out what has continuity and where is critical; one thing certainly worth checking is how they joined the old conduit to a new consumer unit (if they did at all).
I've found MICC transplanted into a plastic CU once with no banjo or anything. That was in a church too thinking about it....
 
True, although it's scheduled for January. I did ask if there was room or could we repull the cables with T&E but apparently the conduits are full and it's not an option. How that works for heat dissipation is another question.
You may well be able to rewire with a CPC using singles as a bunch of them is more compact and flexible than T&E and if lighting circuits then heat hardly a problem, especially with LED lights now. Circuits for electric heating are going to be your biggest issues.

But fundamentally without a CPC/earth you don't have ADS - the RCBO will disconnect on a current imbalance (you hope) and that could well be through somebody's body and not when a fault first occurs.

Also RCBO can fail/stick, and then you really have no protection at all. With a CPC the thermal/magnetic aspect ought to still fire.

Chances are there are only a few screwed up joints and CPC bonding over them would restore much of what is needed. But it will need a systematic check of what is connected to what still, and how to complete it back to the distribution board.
 
Churches are getting into the same class as pubs and farms for dodgy installations.
And just as dodgy EICR's

A few years back I was asked to have a look at an EICR that had recently been carried out at the local church as my wife is on the church PCC and the EICR didn't seem right to the guy that looks after the church one of the observations that was flagged as a C2 was a lack of switches on the unswitched socket outlets
RCBO suitable for circuit with no earth? 1653334554576 - EletriciansForums.net
RCBO suitable for circuit with no earth? 1653334634930 - EletriciansForums.net
the only other observation was a lack of RCD's which was correct due to the old 3036 Wylex boards, having previously been in the church I knew of 3 - 4 observations off the top of my head that would get C2's that had no mention although the EICR only took them a little over 2 hours so not much chance to find much although to miss the array of 951 earth clamps in a very poor state and the metalclad live and neutral fused sevice head on the incomer shows what level they were at
I ended up doing another EICR and found 6 C2's and around 10 C3's and got tasked with doing the remedial works
Looking back through the building file all the previous EICR's dating back to about 2000 the last decent EICR was back in 2004 / 5 when an amount remedial work was carried out after that they were all extremely close copies of the previous EICR upto the end of 2020
 
Churches don’t need any electrical testing.
IN GOD WE TRUST is the motto I think.
therefore surely he has sorted it?
 
Churches don’t need any electrical testing.
IN GOD WE TRUST is the motto I think.
therefore surely he has sorted it?
I reckon he must have been quite pi55ed off with a few of them then as I can think of several church fires caused by electrical faults!
Most recent was July this year....

RCBO suitable for circuit with no earth? 1668899110463 - EletriciansForums.net
 

Reply to RCBO suitable for circuit with no earth? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock