Search the forum,
Discuss Rcbo tripping in the UK Electrical Forum area at ElectriciansForums.net
Without being there and being able to test and inspect, I can't say why it happened, but what I can say is you most definitely should not be removing the main earth with the power on.
Just to add a little to @SparkyChick
if you remove the main earth cable whilst the board is energised, it is possible under some circumstances (not unlikley) that the earth bar and any earthed metal fittings in the property become LIVE at any voltage up to the incoming phase voltage.
it puts a black mark on your reputation if the homeowner drops dead in the shower because you have removed the earth cable, and I expect the paperwork would be a nightmare.
1) Very bad practice to disconnect the main earth without isolating the supply
2) As @Vortigern asks, it might be a RCBO with a "functional" earth for this sort if fault (I think it is really for open N, but hey-ho, both lead to N-E volts).
3) There may be dodgy insulation somewhere and allowing the CPCs to float was enough to cause leakage somewhere.
Reply to Rcbo tripping in the UK Electrical Forum area at ElectriciansForums.net
Hi just wondering if someone can help me. I have an rcbo that keeps tripping but only when the fly earth and neutral lead on the bars it trips...
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently...
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...