Search the forum,
Discuss Rcbo with higher than permitted zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yes, not very good design but equally not dangerous.
The Zs is higher than UK regs on OCPD alone but given your 32A C-curve trip range for 230V covers Zs = 1.1*230/(5*32) = 1.58 ohms best-case down to 0.8 * 0.95 * 230 / (10 * 32) = 0.54 ohms worst-case, your measured 0.83 is going to be met for over half the tolerance range, and the RCD side always met.
Agree, with the Rcd in circuit, R1+R2 tests, its compliant not ideal but ok.
The worry I have these days is that the lesser experience electricians, we’ve a high Zs reading put a Rcd on it.
Without the relevant tests it’s a major concern, days gone by you would certainly fix the problem
Exactly, if it is just a rather long cable then it is not so serious, even though it is probably not meeting the VD spec either. But it could be something more serious that ought to be fixed (bad joint, etc) and not simply side-stepped with the RCD aspect.
Thank you all so much for the replies
And sorry for late response I'm working away at the moment and haven't had much time or that good internet connection I had noted on cert that it was a poor design and there is a few other issues I am due to go back and rectify once I am working back local thanks again the collective hive mind
Reply to Rcbo with higher than permitted zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
OLDBOY
O
Ring main was on a c40 rcbo so I tested the circuit everything was fine and dropped down onto a b32, It’s quite a long circuit but only serves...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
As a retired electrician, I need to specify a new type B board for a village church. Principal load is heating. Ipfc phase to phase is 1.1kA...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...