winayetun

DIY
Reaction score
0
When replacing a light housing, I found the RCCB was somehow tripped. I first used a pen tester to check the wires and found them normal (no voltage). I then used a multimeter to test again. Here are the results:

L-N 7.4 v
L-E 6.8 v
N-E 3 V

After the RCCB was tripped, the readings were zero. So, I think the readings were real.
Only N-E would trip the RCCB, other combinations wouldn't.

Any guess what's going on here?
 
Recommend an electrician with proper testing gear.
On here, we're just guessing and it could cause you more problems.
 
The RCCB detects an imbalance in current between the L & N. It does not matter if that is due to a L-E fault or a N-E fault.

The former is usually more dangerous as it could be someone getting an electric shock, the latter is not as common (less chance of poor insulation breaking down due to low voltages) but is often responsible for difficult to find spurious trips of RCD as systems with a normally very low N-E difference might only see enough stray imbalance current on the occasional heavy load.
 
To make it absolutely clear, taking the title of the post " RCCB tripped when neutral - earth touching" it's supposed to, that is what it's there for to detect an imbalance between the earth and live conductor.
 
I think the OP is probably asking why there were some voltages measured on a 'dead' cable and how come that same 'dead' cable could trip a RCCB?

There's a few things about why you got some readings, but firstly you need to know that you NEVER rely on a pen stick for safe isolation!

The most likely reason that there were a few odd volts here and there is because there were - either through what we call induced voltage (commonly seen on two way lighting circuits and where multiple cables run along each other) and/or the switch itself is not fully isolating/internal arcing. MCB's tend to have a larger internal gap space than a 50p faceplate switch.

There is normally always something floating around on what you perceive as a 'dead' neutral unless it's actually been fully disconnected (or is via a two-pole isolator which is unusual in a domestic situation) and so as others have said, the RCCB has enough to compare the two and will disconnect.
 
The thing to remember is that 'isolating' a circuit using the circuit breaker only disconnects the live. The neutral is still connected and the RCD or RCCB is monitoring the neutral, hence the tripping you experienced. I'm not sure of the definitions written in the UK regs but I wouldn't normally consider a circuit to be fully isolated if it was just switched off by an MCB.
 

Reply to RCCB tripped when neutral - earth touching in the DIY Electrical Advice area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock