I am struggling to understand this.

You have a cu, (std switch on incoming) and each outgoing circuit has a combined rcd/afdd - is this correct?

If so where is the overcurrent protection for each circuit (fault and where needed overload)?
As far as I'm aware these are MCB/RCD double pole devices with AFD protection ,these are bespoke boards made especially for the job I'm on . Hope this helps ,but thanks guys and girls I have all the info now .
Regards
Ray
 
Honestly I'm a bit baffled too, I'm aware of a Siemens MCB + AFDD product, and ordinary RCBO's, and some clever lego-like add on units to add AFD protection (see below), but I've never heard of an AFDD and RCD combo without overload protection too.
Prepared to be proved wrong, and intrigued to see a photo.
I'm concerned that I have given you the wrong answer to what might turn out to be the wrong question!

1624559404447.png
 
As far as I'm aware these are MCB/RCD double pole devices with AFD protection ,these are bespoke boards made especially for the job I'm on . Hope this helps ,but thanks guys and girls I have all the info now .
Regards
Ray
Ahh so rcbo/afdd devices NOT rcd/afdd.

They are quite different from rcd/afdd.

I think you need to check exactly what you have as the question you asked doesn't appear to reflect the equipment you have.
 
Honestly I'm a bit baffled too, I'm aware of a Siemens MCB + AFDD product, and ordinary RCBO's, and some clever lego-like add on units to add AFD protection (see below), but I've never heard of an AFDD and RCD combo without overload protection too.
Prepared to be proved wrong, and intrigued to see a photo.
I'm concerned that I have given you the wrong answer to what might turn out to be the wrong question!

View attachment 87051
Hi Tim
I'll send you a pic of the device.
Tomorrow.
Regards
Ray
 
If its for additional protection only you only need to do the 5X test at either 150mA or 250 mA if the 150 don’t comply , though personally i still do all 6 test as its what I’m used to, and it seems a better way to me.
 
If its for additional protection only you only need to do the 5X test at either 150mA or 250 mA if the 150 don’t comply , though personally i still do all 6 test as its what I’m used to, and it seems a better way to me.
Hi it's for fault protection ,and not additional protection ,but thanks anyway
 
Sorry i thought you said its a TN-S Supply , it would only be fault protection if on a TT.
Or if every circuit has been so poorly designed that ADS cannot be achieved by coordination between the device and the EFLI, leading to the use of RCDs for fault protection.
I have a feeling we're not in possession of the full and accurate facts ?
 
Or if every circuit has been so poorly designed that ADS cannot be achieved by coordination between the device and the EFLI, leading to the use of RCDs for fault protection.
I have a feeling we're not in possession of the full and accurate facts ?
Hi these are double pole rcbos with combined Afd ,all I would like is the maximum mS parameters for x1 and X5 for the rcbo ,this is the sole protection ,each individual circuit is covered by one of these .
Regards
 
Excuse particularly verbose answer, to try and clear up some confusion here.
Double pole RCBO's with AFD have three elements:
1) over current protection, same as fuse or MCB
2) arc-fault detection
3) RCD protection (earth leakage)

In BS7671 terms:
-fault protection is deemed to be via circuit's cpc, earthing, bonding and the fact that fault would operate the over-current element (same as fuse or normal MCB)
-the RCD element is providing additional protection.

The thing that seems to be causing confusion is that while the whole device is part of the circuit's fault protection, the RCD element is deemed to be additional protection.
I think most of the above is already understood and its just a terminology thing.
all I would like is the maximum mS parameters for x1 and X5 for the rcbo
x1 = 300ms
x5 = 40ms
 
Excuse particularly verbose answer, to try and clear up some confusion here.
Double pole RCBO's with AFD have three elements:
1) over current protection, same as fuse or MCB
2) arc-fault detection
3) RCD protection (earth leakage)

In BS7671 terms:
-fault protection is deemed to be via circuit's cpc, earthing, bonding and the fact that fault would operate the over-current element (same as fuse or normal MCB)
-the RCD element is providing additional protection.

The thing that seems to be causing confusion is that while the whole device is part of the circuit's fault protection, the RCD element is deemed to be additional protection.
I think most of the above is already understood and its just a terminology thing.

x1 = 300ms
x5 = 40ms
Exactly!!!

Just because the combined device (rcd, mcb, & afdd) is the sole protection device, doesn't mean every aspect is the primary protection

The mcb aspect provides ADS.
The rcd aspect only provides additional protection in this case as ADS is provided by the mcb aspect.
The Afdd aspect is again additional protection although not under the same regulation as the rcd aspect.

This is important as when you complete the eicr or eic the rcd additional protection should be ticked and NOT the rcd as fault protection

This latter aspect should only be ticked/used if ADS cannot be provided without use of the rcd.
 
Excuse particularly verbose answer, to try and clear up some confusion here.
Double pole RCBO's with AFD have three elements:
1) over current protection, same as fuse or MCB
2) arc-fault detection
3) RCD protection (earth leakage)

In BS7671 terms:
-fault protection is deemed to be via circuit's cpc, earthing, bonding and the fact that fault would operate the over-current element (same as fuse or normal MCB)
-the RCD element is providing additional protection.

The thing that seems to be causing confusion is that while the whole device is part of the circuit's fault protection, the RCD element is deemed to be additional protection.
I think most of the above is already understood and its just a terminology thing.

x1 = 300ms
x5 = 40ms
Hi Tim
Thank you so much for this ,please can you tell me where these measurements are quoted in the regs book ,and as far as filling in the test sheets ,am I measuring on x1 or X5 .
Regards
 
Hi Tim
Thank you so much for this ,please can you tell me where these measurements are quoted in the regs book ,and as far as filling in the test sheets ,am I measuring on x1 or X5 .
Regards
643.8

Or table 3A (only really applicable to fault protection as only the 40ms aspect is required for additional)
 
Go on then, only because it's Friday....
Regulation 643.8 on page 235 describes testing RCD's, see note underneath for the 40ms.

The time/current criteria they need to come up to relevant standards is in Appendix 3, page 363
 