If its for additional protection only you only need to do the 5X test at either 150mA or 250 mA if the 150 don’t comply , though personally i still do all 6 test as its what I’m used to, and it seems a better way to me.
 
If its for additional protection only you only need to do the 5X test at either 150mA or 250 mA if the 150 don’t comply , though personally i still do all 6 test as its what I’m used to, and it seems a better way to me.
Hi it's for fault protection ,and not additional protection ,but thanks anyway
 
Sorry i thought you said its a TN-S Supply , it would only be fault protection if on a TT.
Or if every circuit has been so poorly designed that ADS cannot be achieved by coordination between the device and the EFLI, leading to the use of RCDs for fault protection.
I have a feeling we're not in possession of the full and accurate facts ?
 
Or if every circuit has been so poorly designed that ADS cannot be achieved by coordination between the device and the EFLI, leading to the use of RCDs for fault protection.
I have a feeling we're not in possession of the full and accurate facts ?
Hi these are double pole rcbos with combined Afd ,all I would like is the maximum mS parameters for x1 and X5 for the rcbo ,this is the sole protection ,each individual circuit is covered by one of these .
Regards
 
Excuse particularly verbose answer, to try and clear up some confusion here.
Double pole RCBO's with AFD have three elements:
1) over current protection, same as fuse or MCB
2) arc-fault detection
3) RCD protection (earth leakage)

In BS7671 terms:
-fault protection is deemed to be via circuit's cpc, earthing, bonding and the fact that fault would operate the over-current element (same as fuse or normal MCB)
-the RCD element is providing additional protection.

The thing that seems to be causing confusion is that while the whole device is part of the circuit's fault protection, the RCD element is deemed to be additional protection.
I think most of the above is already understood and its just a terminology thing.
all I would like is the maximum mS parameters for x1 and X5 for the rcbo
x1 = 300ms
x5 = 40ms
 
Excuse particularly verbose answer, to try and clear up some confusion here.
Double pole RCBO's with AFD have three elements:
1) over current protection, same as fuse or MCB
2) arc-fault detection
3) RCD protection (earth leakage)

In BS7671 terms:
-fault protection is deemed to be via circuit's cpc, earthing, bonding and the fact that fault would operate the over-current element (same as fuse or normal MCB)
-the RCD element is providing additional protection.

The thing that seems to be causing confusion is that while the whole device is part of the circuit's fault protection, the RCD element is deemed to be additional protection.
I think most of the above is already understood and its just a terminology thing.

x1 = 300ms
x5 = 40ms
Exactly!!!

Just because the combined device (rcd, mcb, & afdd) is the sole protection device, doesn't mean every aspect is the primary protection

The mcb aspect provides ADS.
The rcd aspect only provides additional protection in this case as ADS is provided by the mcb aspect.
The Afdd aspect is again additional protection although not under the same regulation as the rcd aspect.

This is important as when you complete the eicr or eic the rcd additional protection should be ticked and NOT the rcd as fault protection

This latter aspect should only be ticked/used if ADS cannot be provided without use of the rcd.
 
Excuse particularly verbose answer, to try and clear up some confusion here.
Double pole RCBO's with AFD have three elements:
1) over current protection, same as fuse or MCB
2) arc-fault detection
3) RCD protection (earth leakage)

In BS7671 terms:
-fault protection is deemed to be via circuit's cpc, earthing, bonding and the fact that fault would operate the over-current element (same as fuse or normal MCB)
-the RCD element is providing additional protection.

The thing that seems to be causing confusion is that while the whole device is part of the circuit's fault protection, the RCD element is deemed to be additional protection.
I think most of the above is already understood and its just a terminology thing.

x1 = 300ms
x5 = 40ms
Hi Tim
Thank you so much for this ,please can you tell me where these measurements are quoted in the regs book ,and as far as filling in the test sheets ,am I measuring on x1 or X5 .
Regards
 
Hi Tim
Thank you so much for this ,please can you tell me where these measurements are quoted in the regs book ,and as far as filling in the test sheets ,am I measuring on x1 or X5 .
Regards
643.8

Or table 3A (only really applicable to fault protection as only the 40ms aspect is required for additional)
 
Go on then, only because it's Friday....
Regulation 643.8 on page 235 describes testing RCD's, see note underneath for the 40ms.

The time/current criteria they need to come up to relevant standards is in Appendix 3, page 363
 

Reply to RCD/ combined afdd breakers in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
I have just popped out to a frustrated customer who has had intermittent tripping of a 30mA RCD for years, on average 5 - 10 x p/month. It used to...
Replies
31
Views
4K
Afternoon all, As we all know the new 18th certs only have the facility to record the x1 trip time of a circuits RCD in the test results page...
Replies
4
Views
28K
Deleted member 26818
D
Plumber changes boiler and RCD main switch starts tripping at various times when its firing up or soon after. (I was there doing other work). I...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock