The Cables were not isolated at the CU, so if it is a cable or JB or accessory that is breaking down, it would still allow enough leakage to affect your readings.

Don't forget that MCB's are single pole (in the UK at least) and don't in general isolate the N.

have some more time tomorrow to investigate , just did nt think the conductor insulation would have any bearing if not under load, thanks for the replies..
 
morph,
This has been done recently, it is a function of the meter.
They are basic.
You are testing a capacitor in parallel with the RCD at the sockets, not the RCD itself.
 
morph,
This has been done recently, it is a function of the meter.
They are basic.
You are testing a capacitor in parallel with the RCD at the sockets, not the RCD itself.

true indeed had not thought of that ,
generaly though the variance is not so significant
 
In other words the only meaningful values on a RCD test, are those taken at the CU. Tests taken at the socket outlets only basically prove the RCD is functioning, NOT the operating values of the RCD device!!!
 