Hi morph,

What I would be doing (in the absence of a EL clamp), would be to start disconnecting (both L and N) of individual circuits one at a time, and repeating the Ramp test, to see where it improves, then IR test the suspect circuit/s, average readings on ramp tests for 30mA RCD's tend to be around the 20-25mA mark IME,

Or do as above but IR test each individual circuit to find the culprit/s.

agreed , i have now been asked to sort up stairs socket issue so i will fix that and then look at I/R
it was just the fact that with other circuits isolated and most things unplugged on down ring that the ramp was 8 and 19 at board that seemed odd
if nothing is on how does the ramp result vary so much ?
 
Issue a danger notice.

Appliances will work fine with reverse polarity, but that does not diminish the danger. Such is the danger that modern electronically controlled boilers are designed to detect reverse polarity and will go straight into lock out, thus forcing the owner to call in expert help.
 
if nothing is on how does the ramp result vary so much ?

The Cables were not isolated at the CU, so if it is a cable or JB or accessory that is breaking down, it would still allow enough leakage to affect your readings.

Don't forget that MCB's are single pole (in the UK at least) and don't in general isolate the N.
 
The Cables were not isolated at the CU, so if it is a cable or JB or accessory that is breaking down, it would still allow enough leakage to affect your readings.

Don't forget that MCB's are single pole (in the UK at least) and don't in general isolate the N.

have some more time tomorrow to investigate , just did nt think the conductor insulation would have any bearing if not under load, thanks for the replies..
 
In other words the only meaningful values on a RCD test, are those taken at the CU. Tests taken at the socket outlets only basically prove the RCD is functioning, NOT the operating values of the RCD device!!!
 

Reply to RCD Conundrum in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
377
I'm interested how you would all approach this one. A 3 phase distribution board on a caravan site, under lock and key. Only warden and manager...
Replies
12
Views
346
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
I sorted the fault fairly quickly as it happens but only because I'd come across it once before and at the time a few people said it couldn't...
Replies
13
Views
355
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock