What I would be doing (in the absence of a EL clamp), would be to start disconnecting (both L and N) of individual circuits one at a time, and repeating the Ramp test, to see where it improves, then IR test the suspect circuit/s, average readings on ramp tests for 30mA RCD's tend to be around the 20-25mA mark IME,
Or do as above but IR test each individual circuit to find the culprit/s.
agreed , i have now been asked to sort up stairs socket issue so i will fix that and then look at I/R
it was just the fact that with other circuits isolated and most things unplugged on down ring that the ramp was 8 and 19 at board that seemed odd
if nothing is on how does the ramp result vary so much ?