Switch your meter over to Ohms after the IR test and find out what it is reading.

The RCD will detect a earth neutral imbalance but if the ohms reading is over 7666 ohms the RCD will most likely hold.

230/0.03 = 7660.

Now when you find what it is reading you will have to start spliting the cct to find the problem as its well under 1Meg from your IR test !
 
common for n/e fault not to trip rcd until load applied, ir the ring and break it down till fault located
 
Thanks for your help. The answer to my question is pretty obvious now you mention it. Sincerely appreciated.
 
Another thing to remember, is that with TN-C-S, the earth and neutral are connected at the head.
Only way to see if there is continuity between the earth and neutral in the installation, is to ensure the neutral is disconnected.
You need the main switch off, not just the MCB.
 