tony mc
Switch your meter over to Ohms after the IR test and find out what it is reading.
The RCD will detect a earth neutral imbalance but if the ohms reading is over 7666 ohms the RCD will most likely hold.
230/0.03 = 7660.
Now when you find what it is reading you will have to start spliting the cct to find the problem as its well under 1Meg from your IR test !
The RCD will detect a earth neutral imbalance but if the ohms reading is over 7666 ohms the RCD will most likely hold.
230/0.03 = 7660.
Now when you find what it is reading you will have to start spliting the cct to find the problem as its well under 1Meg from your IR test !