SirKit Breaker
Can someone tell me if an RCD or RCBO, 30ma, will trip on earth leakage if a fault occures from live to the metal case of a switch where no cpc is present ? I think it will as the RCD is looking for an imbalance between line & neutral and this will occure if a person touches the metal switch and provides an earth path.
Any coooment welcome.
Mick
Not quite how a RCD or RCBO is intended to work!! It should trip out before someone touches the live metalwork, and if it is for additonal protection, then it should be within 40mS, at 150mA. 415.1.1 refers.