Doing a little job for a friends of ours who owns a furniture company. Have some metal double sockets round a couple of his work shop areas. Nothing to crazy. Only to be used for fans, kettle, chargers etc.

All in swa clipper along metal tray. No sockets to be used outside and all staff are trained and instructed / competent persons.

Where do you think I stand on RCD protection. As going to have around 8/9 circuits and want to try and save a bit of £££ for not buying rcbos!

cheers people.
 
sockets for general use must be RCD protected unless a documented risk assessment is carried out giving good reason/s for omitting RCD protection. the skilled/instructed persons went out the window with amd. 3.
 
Doing a little job for a friends of ours who owns a furniture company. Have some metal double sockets round a couple of his work shop areas. Nothing to crazy. Only to be used for fans, kettle, chargers etc.

All in swa clipper along metal tray. No sockets to be used outside and all staff are trained and instructed / competent persons.

Where do you think I stand on RCD protection. As going to have around 8/9 circuits and want to try and save a bit of £££ for not buying rcbos!

cheers people.

Yes they need RCD protection unless exempt under a detailed risk assessment, as do all types of sockets up to 20A in any situation or environment apart from where used for connection of a particular item of equipment and labelled or identified as such.

You might want to hint to your mate that trying to circumvent safety aspects of the wiring regs for reasons of cost is not the best way to protect his staff in accordance with the EAWR.
 
And 8 or 9 circuits is a lot of kettles and chargers.
Sacrificing safety for economy is not the best design feature anywhere , but even more poignant in a workshop.
 
As above ^^^^ can't believe he's trying to save money this way especially in a workshop. Anywy, does it need 8 or 9 separate circuits? Daz
 
Whether its an addition or complete new install you may only need 1 - 2 ring circuits so can't see the point of trying to save a few quid by omitting a couple of rcbo's or a new split board if you require room for extra circuits.

If you are the designer insist he has the correct protection gear installed, how much is a life worth and how clear do you want to keep your conscience? :smile5:

Also he may find it voids his public liability if the electrical installation is not up to spec?

Sometimes you have to explain the potential costs involved in the future if he tries to cut corners at this stage.
 

Reply to RCD protection for factory sockets in the Industrial Electrician Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock