Is there such thing as a three phase RCBO??!

Needing to install a three phase circuit for a 8kw three phase heater- connection by a 20a comando

I want to use the metal trunking I will be installing for various 13a sockets- so the circuit doesn't need the rcd protection- but i beleive the 20a comando will..

It will be a new hager TPN dis board

so hows best to get fault and additional protection in TP setup?
 
This any good?
D089B52C-4818-435A-ABD1-5E2B456A0681.jpeg


MK K13435 3phase 415V 5pin with 40A RCD, Commando 32A Socket Rated | eBay - https://www.ebay.co.uk/itm/MK-K13435-3phase-415V-5pin-with-40A-RCD-Commando-32A-Socket-Rated/323637491756?hash=item4b5a4c382c:g:4yEAAOSwQwRb6CsX
 
Could you not fit a 20 amp isolator instead and hard wire the heater in , then you would not need the rcd ? Failing that you could get your customer to do a risk assessment and omit the rcd :)
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

J.C.E

Arms
-
Joined
Location
Earth

Thread Information

Title
RCD protection in a warehouse
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
17
Unsolved
--

Advert

Thread statistics

Created
J.C.E,
Last reply from
Flanders,
Replies
17
Views
3,429

Advert

Back
Top