Afternoon all,

Quick fire question. Can a RCD fused spur still be used for additional protection under the 18th.
I haven’t got my BBB with me and I recall it giving BSEN numbers for devices used for additional protection and RCD spurs not being one.

Job with extra lights and changing board for such a small job is crazy

Thanks
 
Afternoon all,

Quick fire question. Can a RCD fused spur still be used for additional protection under the 18th.
I haven’t got my BBB with me and I recall it giving BSEN numbers for devices used for additional protection and RCD spurs not being one.

Job with extra lights and changing board for such a small job is crazy

Thanks

Yes the changes excluded RCD sockets and FCUs but a recent article in PE pointed out that they were omitted by mistake in the excitement of writing new regulations and this will be rectified in the next publication.
 
Yes the changes excluded RCD sockets and FCUs but a recent article in PE pointed out that they were omitted by mistake in the excitement of writing new regulations and this will be rectified in the next publication.
I have seen that article, however I have also heard from a number of sources that the omission was deliberate as the revised Standard for BS 7288 explicitly states that they cannot provide additional protection and should only be fitted downstream of an RCD to provide additional protection.

Apparently at least one manufacturer of such devices is in talks with BSI around this issue.

So unfortunately I would suggest that the use of RCD FCUs and SRCDs is in fact questionable as things stand.
 
I have seen that article, however I have also heard from a number of sources that the omission was deliberate as the revised Standard for BS 7288 explicitly states that they cannot provide additional protection and should only be fitted downstream of an RCD to provide additional protection.

Apparently at least one manufacturer of such devices is in talks with BSI around this issue.

So unfortunately I would suggest that the use of RCD FCUs and SRCDs is in fact questionable as things stand.
Every SRCD and RCD FCU I have ever fitted has complied with the requirements of 415.1 from BS7671 thus meeting the requirements for additional protection.

What's changed in the product standard that they won't meet the requirements of 415.1 and 643.8 ?
 
Every SRCD and RCD FCU I have ever fitted has complied with the requirements of 415.1 from BS7671 thus meeting the requirements for additional protection.

What's changed in the product standard that they won't meet the requirements of 415.1 and 643.8 ?
I believe there is an explicit statement in the revised BS 7288 that they are unsuitable to provide additional protection. As I don't personally possess a copy of the Standard I cannot verify that.
 

Reply to RCD spur additional protection in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock