Firstly i'll point out that i'm the property owner and the installer of the majority of the electrical fittings in the building, including Main & E7 DB's.
now the history lesson... sorry, but it is relevant
property is 230 years old, I have owned it for 42 years. it was semi derelict at purchase, and i completed most of the rebuild including plumbing & electrics. (i'm not formally qualified in either trade)
building was wired to the existing standards (1978) at the time. and i opted to include E7 as the means of heating.
The system was checked and signed off by a qualified engineer, and the 'electricity board' engineer when meter was fitted.
The E7 DB connected to 6 individual points and 6 heaters of varying capacity were fitted. and the system worked well and reliably.
10 years after installation, i opted for a different heating system and the ESH's were removed, and that side of the system became redundant, though DB and points remained.
approximately 3 years ago the meter was changed, and, as far as i was aware, everything worked ok.
had the odd rcd trip over the years, don't you just love rogue tripping!, on 2 occasions traced to slugs in sockets in the conservatory would you believe... also damp in a JB .... apart from that no probs.

a month ago She Who Must Be Obeyed, decreed that we should have an ESH in the living room and another in the dining room (we won't go into the why's and wherefores right now, i'm just the labourer round here )
so.... ordered 2 nice dual input ESH's (Newlec, but Dimplex by another name), and duly fitted them....
i noted that they required a second (peak) supply into a fused DP point, so put them in as well.

connected the whole shebang up, all seemed great, until the next morning when i noted the rcd had tripped overnight., as E7 was still live, i isolated both ESH's and reset the trip, fine , stayed set ok.
switch on either ESH and the rcd trips.

well, seems i've cocked something up, so, check and recheck all ESH connections... all done by the book, and no obvious errors.

next i make up a cable to connect NSH direct to 24hr supply ..... works fine, no tripping, left for 2 hours for heater to warm up... all ok.

ok, the E7 DB is forty years old and running on 20a cartridge fuses and 60a mcb, (none of which are tripping by the way), so i fit a nice new DB with 100a mcb and 6 20a mcb's ... it would have had to be changed sooner or later anyway.

and we still have the rcd tripping! ....

nothing else, just the main rcd, and if the mcb's for each ESH are isolated then all is ok... and that is just removing live from the circuit, so what can be causing the problem? .... the only thing that has changed from when the old ESH's were removed to when the new ones were installed is the METER ...

going to need some help here guys....
 
Hi - without the benefit of a wiring diagram or pic, I’m going for a guess that when you’ve recently added the peak supply it has resulted in a second path, a shared N effectively. Some of the current (from the circuit with the tripping RCD) now has another path back to the N bar that bypasses the RCD.
 
As above, it sounds like there is an interconnection or borrowed neutral between the E7 and 24h feeds to the heater, resulting in current from one line returning to the other neutral.

Do I understand correctly the two feeds are still from separate DB's? If so, there is a potentially hazardous situation at the moment of one DB back-feeding the other through the interconnection in the heater, so one DB and all circuits connected to it might still be live (both L & N w.r.t earth) when its main switch is off and none of the connected loads are operational. Therefore I would isolate both DBs / heaters and at once until the two feeds to each heater can be proven electrically separate.
 
thanks for your replies, the only thing that has changed since the old heaters came out is the meter, and looking at the neutral path both DB's neutrals go to a common JB (i.e. the incoming neutral, neutral to main DB and neutral to E7 all on the same bus. and my thinking is.... if it was a neutral issue, then the trip would still pop once the offending mcb was switched off?
i have double checked the connection (probably treble checked) on the heaters as you are correct, there is no difference between the 24hr connection and the E7 connection, and legends are small and almost unreadable when kneeling down and peering in the side, but i'm confident that they are correct.... (even i can't get them both wrong)... and the heaters are up and active with the 24hr connection on.
yes, i'll upload some pics just as soon as i work out how to do it :-).

as i'm an amateur, i have contacted a proper electrical engineer who has all the proper tools and knowledge, who will visit me on monday..

i'm sure there is no backfeed path, the connections at the heater are correct and separate.
(one presumes that dimplex would not strap them together ).

also, with the 24hr connection off (dp fused switched outlet), the heaters will still trip the rcd....

but not if i do a temp connection to the 24hr side.

as i said, i'm no expert, and certainly bow to the collective wisdom of you guys on here, but this (to my simple mind) is not rocket science, there is a simple answer just waiting to be hit upon. with the correct equipment and experience.

my thinking is .... meter is only thing to have been changed ... but connections look ok
rcd may be too sensitive, it's 30 years old .. but then why doesn't it trip when heaters wired to 24hr circuit ......

i have spent the last 50 years repairing computers and networks, so fault finding techniques are not alien to me (remember 'divide and rule')... so i'm pretty sure i have done as much as i can without proper test equipment.
 
this morning, whilst E7 was live, i isolated the 24hr feed to the heaters (by switching off at the DP switched outlet), then switched on the E7 DP sw to each ESH. as soon as i tried to make the mcb for either heater the rcd tripped.

just saying :)
 
How many rcds do you have? My reading of your posts is just one 'up front'.

If it is one up front could you jot down and post what it says on the label on it? Or post a photo of it. Does it look like the attached image - a voltage operated earth leakage circuit breaker which are superseded these days by a current operated elcb.

Is your home earthed by a rod in the ground?

If you are having difficulty taking photos to post, ask a neighbour's teenager to pop round with their mobile phone and take some for you, and then send them to you by email for you to to use.
 

Attachments

  • elcb.jpg
    elcb.jpg
    4.7 KB · Views: 23
Last edited:
Last edited:
having looked at Marconi s wiring diagram above.

long shot.

could you have wired the 2 standard and night supply neutrals together instead of in there individual terminals.

this would explain your system working when transferred into the standard 24 hour board.

if you had done the above then the return night current would have an alternative path through the daytime neutrals Cu. Thus the imbalance tripping the RCD On the main Day CU.

Is the RCD a double pole isolator or single pole isolator. If it’s a single pole I would guess the night storage heater would continue to work and be warm in the morning. Unless the night tarrif CU is protected by another RCD.
 
as soon as i tried to make the mcb for either heater the rcd tripped.

When referring to RCD trip events, please could you be explicit as to which RCD trips, as I believe there is now one in each CU. It was confusing at first because I think you typed MCB a couple of times where you meant RCD and I have lost track of which device was tripping in the early stages when the old E7 CU was in use. I read it as the RCD in the peak CU tripped when the supply from the off-peak side was energised but perhaps that was not what you meant.

If in fact the RCD on one side is tripping when the other side is energised, and there is no cross connection, one possibility is that there is an existing neutral-earth fault on the side that trips, that only causes enough leakage to trip when the heater's control unit switches on load in response to the other supply coming on.
 
thanks for your enquiries ..
the property is earthed by a rod
there is only 1 rcd (marconi.... one of the things i am COMPLETELY ok with is computers, having worked in IT for 50 years, so i won't be needing a teenager from next door to help me out :) )
here's a pic of the rcd (was changed from voltage to current 15 years ago)
luciens... only the one rcd ... as per pic, (apologies for the 'cut out' legend.... thats for SWMBO in case i'm not at home and it trips for some reason, like when she dropped the steam iron on the floor a month ago :) )
the untidyness in the wiring is due to ongoing 'mucking about, trying to fix it' work.
today i'm going to remove the E7 (live) tail from the meter (pic of meter to follow) and stuff it into the main JBox (i.e. the E7 CU will now be connected to the 24hr supply, and in all respects the same as the main CU.)
havn't had so much fun since i broke my leg ....
 

Attachments

  • rcd.jpg
    rcd.jpg
    122.6 KB · Views: 38
  • meter.jpg
    meter.jpg
    81 KB · Views: 37
Need a wider picture of the full set-up. Something doesn't seem correct, assuming the service terminal block is outgoing from the rcd it has five conductors connected which seems wrong. It appears one conductor bypasses the rcd.
Is the meter above left of the rcd, I suspect the line to your E7 is not rcd protected but the neutral is going through the rcd.
 
Last edited:
hi westward thanks for your reply
yes, the meter is above left of the rcd.
the 5th (far right) connection on the meter is the E7 live o/p, this goes direct to the E7 CU.
so what you see at the service JB, as you correctly point out is live & neutral from the rcd, live & neutral to the main CU, and lastly neutral to the E7 CU
[automerge]1573126646[/automerge]
Need a wider picture of the full set-up. Something doesn't seem correct, assuming the service terminal block is outgoing from the rcd it has five conductors connected which seems wrong. It appears one conductor bypasses the rcd.
Is the meter above left of the rcd, I suspect the line to your E7 is not rcd protected but the neutral is going through the rcd.
you're quite correct, and this was how it was left after the new meter was fitted.
are you suggesting that i fit a second rcd for the E7 circuit, so that (as far as the E7 circuit is concerned) both live & neutral go via an rcd ?
 
Last edited:
That is your problem. The line and E7 neutral are creating an imbalance as one uses the rcd while the other does not. If you have a TT system and that is the only rcd then the E7 circuits a not likely to have fault protection. The E7 needs a separate rcd with its neutral taken from before the current rcd.
[automerge]1573127713[/automerge]
This is the set up you require.
20191107_115355.jpg
 
Last edited:
That is your problem. The line and E7 neutral are creating an imbalance as one uses the rcd while the other does not. If you have a TT system and that is the only rcd then the E7 circuits a not likely to have fault protection. The E7 needs a separate rcd with its neutral taken from before the current rcd.
ok, that makes sense to me... and easily done, apart from taking the neutral prior to the current rcd .... there is no available (extra) connection point, unless i fit a JB into the incoming neutral line ?

will nip off and get required bits...
 
You need another single pole service terminal block. At this point you need the services of an electrician as you are touching wiring which strictly speaking can only be isolated by an authorised person.
 
It's a pity we didn't have that pic to start with. The OP did stress that the only thing that had been changed recently was the meter, but I suppose we all overlooked something so blatant as the tails being connected up wrongly, which could never have worked.
 
The E7 line which bypasses the rcd does seem an alteration, black cable tie fitted. I suspect this has nothing to do with the meter change. I suspect when the rcd was fitted to replace the voltage operated device some time back the E7 was no longer in use so no problem was evident.
 
ok guys, thanks for all the advice, and I will be taking it. i have all the gear (and some idea :) ), so i will make the connections today, and if it all works ok, i will still leave the appointment for local sparks to come monday pm.... and he can check it over for cockups and poor workmanship, and sign it off ..... (hopefully) ...

i'll post results tomorrow ... should i still be alive ....
 
It's naughty, whichever way it came about. With any load on the E7 board, in the event of a trip the house blacks out, but every single point is still live, both on the E7 and the 24h and there is more risk of shock with the RCD off than on. It's a good thing it was self-incriminating.
 
It's naughty, whichever way it came about. With any load on the E7 board, in the event of a trip the house blacks out, but every single point is still live, both on the E7 and the 24h and there is more risk of shock with the RCD off than on. It's a good thing it was self-incriminating.
it's a good point.... but, as it stands, with the rcd tripped, the only live would be to the E7 cct, both live & neutral to the 24h cct would be isolated.
[automerge]1573134350[/automerge]
That is your problem. The line and E7 neutral are creating an imbalance as one uses the rcd while the other does not. If you have a TT system and that is the only rcd then the E7 circuits a not likely to have fault protection. The E7 needs a separate rcd with its neutral taken from before the current rcd.
[automerge]1573127713[/automerge]
This is the set up you require.View attachment 53677
great!.... got the bits, just consuming last supper (well, lunch actually) and i'll be at it !
 
as it stands, with the rcd tripped, the only live would be to the E7 cct, both live & neutral to the 24h cct would be isolated

No they wouldn't, if there's load on the E7 DB, that's why it's so dodgy. There's a path from E7 line, through the E7 load to the E7 neutral bar (which is now at 230V w.r.t earth), via the splitter block to the 24h neutral bar also now at 230V, through the 24h load to the 24h line. There's no circuit to supply neutral so none of the loads work and it all looks dead as a dodo, but every conductor in the installation is sitting at 230V via the loads. The resistance of a heater in series makes no practical difference to the severity of an electric shock. And there's no RCD protection.
 
No they wouldn't, if there's load on the E7 DB, that's why it's so dodgy. There's a path from E7 line, through the E7 load to the E7 neutral bar (which is now at 230V w.r.t earth), via the splitter block to the 24h neutral bar also now at 230V, through the 24h load to the 24h line. There's no circuit to supply neutral so none of the loads work and it all looks dead as a dodo, but every conductor in the installation is sitting at 230V via the loads. The resistance of a heater in series makes no practical difference to the severity of an electric shock. And there's no RCD protection.
yes, unless all the mcb in the E7 CU are off
[automerge]1573145473[/automerge]
I would get an electrician in to give the installation a thorough check. For your own peace of mind.
he was coming monday pm anyway... so (by law, i believe) i need to have it checked out for cockups and/or poor workmanship
[automerge]1573146087[/automerge]
how better to spend a wet afternoon ....
neutral split via new JB, new rcd fitted (80a) new tails where needed.
ccts are independant of each other now, each with own rcd.
what can possibly go wrong ? :)
thanks for your help guys, hopefully SWMBO will be nice and warm tomorrow, and i'll have lots of brownie points ....
will report back in the morning
 

Attachments

  • e71.jpg
    e71.jpg
    96 KB · Views: 27
  • e72.jpg
    e72.jpg
    90.6 KB · Views: 26
Last edited:
ok.... system working fine (well, apart from the fact that i failed to switch on one of the heaters ... doh) .... i checked them at 4 this morning (and switched on the one i left off last night !).
So, big thanks to you guys... saved me a lot of time and money, although i will still get it all checked by Mr Sparks on monday.
on reflection.... i'm a bit ----ed off with whoever fitted the new meter, and left the system in a dangerous state, i'm just lucky that i had no loads on the E7 side and the mcb was off. AND it cost me £100 plus to remedy, on the plus side thankfully no-one got hurt....
thanks again
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Norfolk uk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
RCD tripping when E7 switches on
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
37
Unsolved
--

Advert

Thread statistics

Created
problems,
Last reply from
problems,
Replies
37
Views
4,303

Advert

Back
Top