Can you confirm you are carrying out these works in Southern Ireland as it will be inappropriate to advise you carrying out illegal works.
 
When the OP said 'garage' in his first post, I was expecting something like a 4 or 6 module enclosure, with a RCD doubling as the main switch, and 2 or 3 MCBs.
What we have is a 20 module enclosure, already fitted with 7 MCBs and room for 10 more. Are we talking garage, as in a small room where someone might park their car, or more likely use to store junk, or garage, as in a business the repairs and services cars?
There also doesn't appear to be an incoming cable of the sort of size I'd expect for a 20 module enclosure.
 
Well spotted! As it is now the busbar is fed by the neutral from the RCD.
Whist not being able to make out how the DB is configured I dont think the above is correct, there appears to be a brown tail connecting into the top rail busbar at the base of a 20a mcb. However a SP 100a isolator on the lower rail and it being unclear where the supply connects is mystifying. Regardless of legality the OP should seek professional assistance before going any further.
 
Yes, was wondering about the SP isolator as it is not something I have ever seen before, even for sale let alone installed, it has always been DP for single-phase isolation switches.

Really the OP needs to get a registered contractor in for this work.
 
Whist not being able to make out how the DB is configured I dont think the above is correct, there appears to be a brown tail connecting into the top rail busbar at the base of a 20a mcb. However a SP 100a isolator on the lower rail and it being unclear where the supply connects is mystifying. Regardless of legality the OP should seek professional assistance before going any further.
Ah yes I see it now.
 
can't see anything in the top terminals od the RCD and the screws look askew as if the cage has never been tightened. apart from which, as westie says in ROI i think it's illegal, and just to be blunt without causing offence, it's a mess.
 
I don't mean to be cruel since i'm all for people doing it themselves as long as they definitely know what they're doing, but there are some really iffy practices going on in this box - tape on what i presume is a split live cable, no sleeving on a fairly long piece of cpc, junction boxes used to join cables, cables strained into connections on angles and some excess copper showing. Not massive thing but would expect a neater tidier job for a new installation - my point is this points to that you might have made other mistakes in other areas. Get a pro in.
 
Not familiar with the Garo boards, but looks like those MCB's by the RCD are switching the Neutral.
Also the cable used is not suitable for Republic of Ireland as the CPC should be the same size and insulated throughout.
 
Not familiar with the Garo boards, but looks like those MCB's by the RCD are switching the Neutral.
Also the cable used is not suitable for Republic of Ireland as the CPC should be the same size and insulated throughout.
Daft question, do you follow BS 7671 in R of I?
 