Hi all I recently built a new garage. Wired it myself put up the fuse board but now when I go to plug in any appliance the rcd trips out. Theres nothing else plugged into the sockets. I wonder did I make a mistake wiring the fuse board?11
post a pic of the board with cover off. (isolate first, of course.).
Is it a dual RCD CU?
Hi Limerick and welcome.
Can I ask which RCD is tripping, the one in your new consumer unit, or the one in the house?
Its the rcd in the new garage.
The three neutrals on the right of the right hand neutral bar - what circuits are they from?
Difficult to say Limerick, where are you
' a member close to you may offer to come take a kook see
To me, it looks like the RCD would be on the RH side, and a busbar from the LH RCD live output to the circuit breakers, mounted to the left of the RCD. Now it should work the other way round, provided the cables are adjusted correctly ...
Sorry to bring this up but I have just realised you are in Southern Ireland and unless you are an REC (Registered Electrical Contractor) what you are doing is illegal. @Risteard will confirm this but I am pretty sure I am correct.
To me, it looks like the RCD would be on the RH side, and a busbar from the LH RCD live output to the circuit breakers, mounted to the left of the RCD. Now it should work the other way round, provided the cable are adjusted correctly ...
Well spotted! As it is now the busbar is fed by the neutral from the RCD.
Can you confirm you are carrying out these works in Southern Ireland as it will be inappropriate to advise you carrying out illegal works.
Status
Reply to Rcd tripping in the UK Electrical Forum area at ElectriciansForums.net
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...