No. But they are very closely linked. Unfortunately for the OP, he has carried out work which he is legally not entitled to do, which may explain why the request is on this forum.
I forget you are also in the Republic while I always refer to Risteard ?
 
That's actually the best piece of advice given today. However we are where we are.To solve his electrical issue I would suggest the OP reverse the rcd neutrals. I would also advise he give a little thought to the possible consequences of going public with this post, from a legal and house insurance point of view.
Is that what the problem is then, the neutrals are the wrong way round in the neutral bars?

I can't even tell from looking at it where the neutral is coming from, just looks like two neutrals from the RCD into the neutral bars to me. Where is the neutral from the incoming supply, or am i being dim?
 
I can't even tell from looking at it where the neutral is coming from, just looks like two neutrals from the RCD into the neutral bars to me. Where is the neutral from the incoming supply, or am i being dim?
It's not easy to make it out from the picture. The N bar on the right is where the main neutral comes in. The N bar on the left is for the sockets on the rcd. If you look at the bottom of the rcd he has the incoming live, but instead of the incoming neutral from the main neutral bar, he has inserted the "outgoing" neutral resulting in current going through the rcd in the same direction twice
 
Southern Ireland follow IS 10101:2020 which replaces ET 101:2008 but I believe there was some delay but could be wrong @Risteard will know. Not BS7671.
Yes correct it is I.S. 10101:2020. Currently we are in a transition period. From 1st February any new installation should be designed and constructed to the 5th Edition (I.S. 10101:2020) - installations can continue to be designed to ET 101:2008 (4th Edition) until 31st January. (Although as non-essential construction works are currently closed until at least the end of February realistically new designs now will be to the 5th Edition.)
 
It's not easy to make it out from the picture. The N bar on the right is where the main neutral comes in. The N bar on the left is for the sockets on the rcd. If you look at the bottom of the rcd he has the incoming live, but instead of the incoming neutral from the main neutral bar, he has inserted the "outgoing" neutral resulting in current going through the rcd in the same direction twice
Which wire is the incoming neutral? The 10mm on the right N block goes to the top of the RCD, the 10mm on the left N block goes to the bottom of the RCD, making it look like there is no neutral at all and it's just looping on itself.

I could have this completely ---- up because i'm not used to neutral bars (they confuse me at present) but i genuinely can't see a N feed coming into the unit.

Sorry for the inane questions - i'm a trainee and looking to see if i can figure this out.

OP if you're still here - which wires on the pics are coming from the existing consumer unit?
 