Discuss Rcd in the Australia area at ElectriciansForums.net
L
lamb.a
We are suppling an outside portacabin with a steel wired armoured 3 core cable live neutral earth from a TN-S system. Does the portocabin reguire an earth electrode and does the origin of the supply have to have an rcd/rcbo fitted with a rcd and also fitted on the consumer unit inside the portocabin.
Hey.
We do a lot of portacabins for local schools and the way I do it for TN-S is 25mm3c swa protected by 100mA RCD and 60A switchfuse at the origin then terminated into whatever board is in the cabin. Usually the board in the cabin has a 30mA rcd up front as main switch, I then bond everything back to my DB in the cabin i.e water, gas, steelwork etc, as the 25mm CPC in the swa is sufficient to carry any fault current back to the main intake un the school and de-energise the supply.
For TN-C-S, I do turn them into TT installations i.e 25mm2c and drop a 25mm earth down to my rod, the rest is the same.
Hope this helps.
Reply to Rcd in the Australia area at ElectriciansForums.net
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...