It would mean that only the shower would trip, and not half the circuits in the house.

Wouldn't really tho would it, if both rated at30mA it would be pot luck which one went out first


Even if the other side pops and the shower keeps running, then the shower side will exhibit a difference in current between L and N on that side, and should therefore trip as well.
 
Last edited by a moderator:
Lost me there ringer, still don't get what ur gonna gain from putting it on a rcbo on a split board?
 
Last edited by a moderator:
edit. paul.m is close to you if you get stuck.


"He's off to have a look at it after work" and "its in a pub." Count me in but your driving :).

I'll pm you my number if you need a hand.

First place to look at is that new switch, it worked ok before that was changed? Next step the cu, visual first then an IR test as above, if that's not the problem then clamp meter cpc at the cu as it could be accumulated earth leakage.

You say it trips when the shower on/off button is pushed. Let's have a look at the element, probably the same problem as the dishwasher in the pub.
 