5 5.6Over-current protective device rating exceeds the current carrying capacity of the circuit, feeding multiple outlets / accessories. See Regulations 433.1.1; 533.2.
the electrician is stating you need full rewring and I dont think this is the case. can anyone help and advised what would be the solution to the problem
the electrician is stating you need full rewring and I dont think this is the case. can anyone help and advised what would be the solution to the problem