I wonder if anyone could assist with this query please ? I am a newbie, so any guidance or alternatives would be greatly appreciated.

I need to run a ring final partly against a wall with internal 25mm Celotex type insulation. The additional Celotex being needed due to reduced cavity insulation. Diagram below ! Also fyi, the Celotex and board are separate, not ‘backed’.

I’m trying to decide whether to “1”- clip to the thermal block, flush (with capping), under the Celotex; or “2”-go between Celotex and board, and consider the respective pro’s and con’s of each. …or any other options ?

I’m not 100% sure from the BBB what the reference method would be for the first route. Possibly 103 ? which would affect my ccc somewhat.

Taking route 2 would (might?) need me to channel slightly into the Celotex which is also frowned upon. ….What would you do ?

upload_2019-5-30_11-22-59.png
 
Test Meter - Forum Sponsors since 2007!
This official sponsor may provide discounts for members
Advertisement - Content continues below

Ian1981

-
Mentor
Arms
Esteemed
If the cables are clipped to the thermalite block work then it is more like reference method C , as one side of the cable can loose its heat through the block work and into the cavity of the wall , the cable is not touching one side of the plasterboard in a cavity wall nor is it completely surrounded by insulation in a cavity wall.

Appendix 4 might give a different reference method so it’s worth having a look at it.
 
Last edited:

Wilko

-
Arms
Esteemed
As per @Charlie_ and @Ian1981, I also prefer route 1 against the block work. IMHO this looks most like method 102, which is suficientemente bueno. I think route 2 looks most like method 3, which is no está bien :) .
 
  • Thread Starter Thread Starter
  • #6
If the cables are clipped to the thermalite block work then it is more like reference method C , as one side of the cable can loose its heat through the block work and into the cavity of the wall , the cable is not touching one side of the plasterboard in a cavity wall nor is it completely surrounded by insulation in a cavity wall.

Appendix 4 might give a different reference method so it’s worth having a look at it.
Thanks Ian, I'll have another check over App 4 too
 
  • Thread Starter Thread Starter
  • #7
As per @Charlie_ and @Ian1981, I also prefer route 1 against the block work. IMHO this looks most like method 102, which is suficientemente bueno. I think route 2 looks most like method 3, which is no está bien :) .
Cheers Wilko, and thanks for the Spanish lesson too. I rarely get beyond "dos cervezas por favor"
 
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
Advertisement - Content continues below

Reply to Reference method / routing guidance for cable on a wall with 25mm Celotex in the Electrical Forum area at ElectriciansForums.net

CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members
Advertisement - Content continues below
Advertisement - Content continues below

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Advertisement - Content continues below
Top Bottom