Always good to try and understand what someone else was looking at when they did an EICR…
So, a couple of pictures to help you out.


This is the only fused neutral I can find, so why list it twice…. And why have different codes?
Will change to a lockable isolator as required, sending this old one to Lucien if he wants it.

Thermostat for heating. Cpc through conduit not continued to thermostat itself.
Solutions? First thought was fill the gap with metallic flexible conduit, but this will be imperial sizes. Or fit a metal end box, tap an earth stud on the back and replace 2 single cores here with 3 core flex.
Surprised it wasn’t noticed in all the previous reports…. But then, it took them until 2013 to notice there was no suppliers earthing.
Other issues included a seldom used outside socket. Had been damaged and taped up with duct tape…marked as a C2.