Hi Electrical experts:

I am new here.

Can I remove the sheath from the SER, only inside the conduit, to make it easier to thread the wires through the conduit and go around corners through LB boxes?

I am installing a generator on the side of my house (some 75' away from the Automatic Transfer Switch) and am running both a 4-4-4-6 aluminum SER cable, and also a control cable inside conduit.

In the garage I have the SER and control cable simply exposed, then they go into a conduit then through the wall then along the outside of the house.

To make it easier to bend the wire through the LB boxes, is it OK to remove the sheath and treat the wires like THHN? I would not remove the sheath on the 6 conductor control cable.

I live in the US, Washington specifically.

Thanks, Mark.
 
Hi Electrical experts:

I am new here.

Can I remove the sheath from the SER, only inside the conduit, to make it easier to thread the wires through the conduit and go around corners through LB boxes?

I am installing a generator on the side of my house (some 75' away from the Automatic Transfer Switch) and am running both a 4-4-4-6 aluminum SER cable, and also a control cable inside conduit.

In the garage I have the SER and control cable simply exposed, then they go into a conduit then through the wall then along the outside of the house.

To make it easier to bend the wire through the LB boxes, is it OK to remove the sheath and treat the wires like THHN? I would not remove the sheath on the 6 conductor control cable.

I live in the US, Washington specifically.

Thanks, Mark.
I'm answering from the UK, and have limited recall here 🤔, but I believe stripping the sheath from the cable violates code in several ways - including removing identification information (on the sheath), modifying the cable from its approved state, and removing what little moisture protection is provided by the sheath.
Washington Administrative Code seems to tightly regulate exposed wiring where it's run outside a property, so you don't seem to have many options. Viable alternatives might be increasing the size of the conduit(!), or using a junction box to transition from the SER to THHN/THWN-2 at the start/end of the conduit run.
I wondered about using metal trunking, but apparently that's not regarded as robust enough compared to 'pipe'!
 
I would think its much like the UK, where we have "single core" cables designed to be drawn through a conduit... with physically tougher insulation than that of a wire being part of a multicore cable.
Its tempting just to strip the outer sheath of a cable, to just the inner cores, and pull them through... but as suggested... a joint box at each end to change from one type of cable to another. Just make it accessible for maintenance
 
Thanks for the reply.

I forgot the wires inside the sheath may not be approved for pulling inside a conduit due to insulation strength.

I'll go ahead and shove the big --- wire the rest of the way through the conduit.

I'm half way there now.

Thanks guys.

Mark.
 