Discuss Replacing a gas boiler with electric. in the Central Heating Systems area at ElectriciansForums.net
Soulsurfer
Hi just after a bit of help ref a swap out as above for one of my builders at his home,
He wants to replace gas boiler with an EHC 9kW Comet/Fusion boiler and has been quoted to have necessary 10mm T & E run from new meter to boiler position which is around a metre away.
Thing is I don't have much experience as yet with boiler controls although following S plan or similar is fine but this is on a tariff which is 20 hrs in 24 off peak rate and 4 hours on full rate in 2 x 2 hr bursts.
They have quoted to fit a Danfoss 103-E7 7 day timer which I expect would be fitted in cupboard where boiler is as there is a programmer in there now existing for gas boiler.
There is a normal room stat on wall in hallway too so I'm thinking it's just a case of rewiring the stat and new programmer to the elec boiler as required plus feeding the programmer via a 3A fused SFCU.
would it be best to run the 10mm feed through a DP switch isolator in cupboard next to boiler ? or direct in ? as it looks like the DNO wants a 4 pole switch fitting for the on and off peak supplies after the meter and then 2x 63A mcbs usually out when general service and off peak consumer units are used.
Although as heating only there is not likely a need for extra consumer unit such as with storage heaters in this case.
Any advice appreciated, Thanks
A freestanding convector heater from the DIY shop is also 100% efficient.
Have you explained that it'll cost more to run than gas? Also, he might find the lights dim every time it cuts in depending on how good the dno network is.
Yeah 100% efficient but I still cant see how it will be cheaper to run :) Even the sales gumpf says ideal for replacing LPG or oil. The control Side of things....The boiler has a built in pump and the control connections R and P are Volt free so do not follow a conventional S-Plan diagram other wise your supply 240V to the boiler PCB and damage it. You will have to feed grey of both valves from R in boiler and connect oranges of both valves to P in boiler. This way the volt free switching is switched from the micro switch in the valves... When the micro switched is closed by the room or cylinder thermostat calling for heat, 240V will be supplied to brown of either valve depending on what's been called for, the valve will motor round and close the switch between grey and orange.
On the efficiency side, looking at BG just now they have gas at 3.6p per kWh and elec at 12p. Electric more efficient? Not so much anymore with modern condensing boilers claiming 90% efficiency and internal voltage drop of say 3% there's only 7% difference. Adjusting for boiler efficiency that's 4p for gas. Forget the voltage drop and use the cheapest night rate of 6.5p for leccie and for the same heating I'm expecting him to pay 50% more at least. What have I missed ?
Reply to Replacing a gas boiler with electric. in the Central Heating Systems area at ElectriciansForums.net
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
3 Phase Smart Meter EDMI ES -30 B Install I have a question regarding the potential replacement of my existing EON supplied ELSTER A1140 3...
Having wired in parallel with my cordless programmable room stat an Alexa compatible wifi switch which has failed. I want to have a app...