Hi all,

I have a single surface mounted socket in a cupboard which our freezer is plugged into. We don't have any sockets in our hall which the cupboard is off so I thought it might be useful to change the one gang socket for a two gang, again surface mounted to keep it simple.

Its on our socket ring main and must be a spur as there is only one cable to it not loop in and out. In theory I think all I need to do is remove the old one gang socket and screw on a two gang box in its place, I would just use the existing supply to the old socket.

Assuming I'm right on the above? Seems like a simple job. Any regulations I should be worried about here? Given I'm literally just replacing the surface box and not changing any wiring? Is this notifiable?

Thanks for the advice
 
No, the job is not notifiable.
As long as the existing socket is spurred directly off the ring final circuit and you are competent in undertaking the job I see no problem. Just remember safe isolation (not by a neon screwdriver) The socket needs to be RCD/RCBO protected.
 
Hi all,

I have a single surface mounted socket in a cupboard which our freezer is plugged into. We don't have any sockets in our hall which the cupboard is off so I thought it might be useful to change the one gang socket for a two gang, again surface mounted to keep it simple.

Its on our socket ring main and must be a spur as there is only one cable to it not loop in and out. In theory I think all I need to do is remove the old one gang socket and screw on a two gang box in its place, I would just use the existing supply to the old socket. Suitable checks need to be done prior to just swapping the socket Willy Nilly, an Electrician will be able to check this for you.

Assuming I'm right on the above? Seems like a simple job. Any regulations I should be worried about here? Given I'm literally just replacing the surface box and not changing any wiring? Is this notifiable?

Thanks for the advice
If the existing single socket is truly a spur, and not a spur off another spur the just swap the single for a double. If hower it has been spured from another spurred outlet then more work will be required.
 
As @Pete999 has mentioned, just make sure it's an actual spur from the RFC (Ring Final Circuit) and not a spur of a spur mate.
 
Ok so I've had a closer look at this and noticed something but don't think it affects me converting one gang to two gang. The cable from the ring main goes to a fused switch. From the switch there is a cable out to the socket and a cable out to the ceiling light in the cupboard. The cables terminate at these loads and do not go elsewhere.

Going back to what Pete999 & Spoon said, assuming it is a spur off the ring main is the fact that it is supplying a light and a socket still classed as a single spur? And how do I determine that its not a spur off a spur? In theory it shouldn't be as if the work was done properly then no one should have done that in the first place? I realize you should never assume.
[automerge]1568373712[/automerge]
The fused switch only operates the light as expected and does not cut power to the socket.
 
The cable from the ring main goes to a fused switch.

So in your first paragraph above you are only assuming it wires to the RFC.

Going back to what Pete999 & Spoon said, assuming it is a spur off the ring main is the fact that it is supplying a light and a socket still classed as a single spur? And how do I determine that its not a spur off a spur? In theory it shouldn't be as if the work was done properly then no one should have done that in the first place? I realize you should never assume.

See where this fused switch wires back to.
You can test the circuit to determine what type of circuit it is.
 
So in your first paragraph above you are only assuming it wires to the RFC.



See where this fused switch wires back to.
You can test the circuit to determine what type of circuit it is.
Hmm I can't track the incoming wire as it disappears into the wall, would need to pull up floor boards etc to track it. I do know that when I switch off the MCB to the ring main the light and socket are cut off but that doesn't answer if its a spur off a spur.
 
Hmm I can't track the incoming wire as it disappears into the wall, would need to pull up floor boards etc to track it. I do know that when I switch off the MCB to the ring main the light and socket are cut off but that doesn't answer if its a spur off a spur.

Do you have any test equipment?
 
lost count of the number of times i seen more than 1 socket on an unfused spur. even hold hands up to doing it myself on occasions where the load is low e.g. laptop, phone chargers etc.
 
They said it all
[automerge]1568378377[/automerge]
Ok so I've had a closer look at this and noticed something but don't think it affects me converting one gang to two gang. The cable from the ring main goes to a fused switch. From the switch there is a cable out to the socket and a cable out to the ceiling light in the cupboard. The cables terminate at these loads and do not go elsewhere.

Going back to what Pete999 & Spoon said, assuming it is a spur off the ring main is the fact that it is supplying a light and a socket still classed as a single spur? And how do I determine that its not a spur off a spur? In theory it shouldn't be as if the work was done properly then no one should have done that in the first place? I realize you should never assume.
[automerge]1568373712[/automerge]
The fused switch only operates the light as expected and does not cut power to the socket.
From your description and my guesswork it looks like the light is wired through the LOAD side of the FCU and the socket is wired to the feed side pf the FCU, not an ideal method in my opinion needs checking out by someone competent.,
 
The only equipment I have is a multimeter and Fluke non-contact voltage tester. I ran it past a colleague at work who has done the edition 18 exams and they thought it was ok if its not a second spur but as thats hard to determine maybe I'll just leave it.
 
2 RFC and 1lighting cables by the description???? 1 from the RFC 1 to the new socket and 1 to the light??

It's not totally clear to me from the description, obviously if it is as you describe then the SFCU is already on a spur.
 
There are 3 cables to the fused switch only, supply from RFC (assumed). One cable out to light and one to the socket. From what I have read tonight you should either have a junction box off the RFC to a 13A fused spur or junction box to unfused spur with switching and local protection (sounds like my fused switch) so perhaps what I have is the latter.
 
There are 3 cables to the fused switch only, supply from RFC (assumed). One cable out to light and one to the socket. From what I have read tonight you should either have a junction box off the RFC to a 13A fused spur or junction box to unfused spur with switching and local protection (sounds like my fused switch) so perhaps what I have is the latter.

I don't know where you have read that, but it is not an accurate representation of the regulations.
An unfused spur is a single cable connected to a ring circuit at an accessory or a junction box, this is permitted to feed one, and only one, point. That point can be a single socket twin socket (but not two singles), fused connection unit (FCU) or switched fused connection unit (SFCU)
A fused spur is connected to a ring circuit via an FCU or SFCU, this can supply as many points as you like as long as the cables are suitably sized etc etc.

What you have described is an unused spur feeding two points, the first point is an SFCU and the second point is the socket you wish to change. This is not permitted by the regulations.

Have you confirmed that the circuit is in fact a ring circuit? What is the rating of the circuit breaker which feed it?
 

Reply to Replacing spur one gang socket for two gang in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock