At fist sight it doesn’t sound like there is anything technically wrong; just a difference between what you thought you were getting/asking for and what the sparks did?
 
A note on point 3 - a spur, and rules on spurs from spurs etc only really apply to ring final circuts. This is because the protective device is sized for overload protection of two cables in parralel (each leg of the ring) and a spur wired in a single cable from this point would not be suficiently protected from overload.

A radial circuit (it sounds like this is what you have) can be split and branched off at any point, providing it is not overloaded.

Do you have 2 16A circuits? One for upstairs and one for down? If you have a seperate 3rd circuit for the kitchen (idealy 32a) you will probably have no issues with overloading. Things that could cause problems would be large loads such as heaters, tumble dryers, irons and possibly vaccum cleaners. But this should have all been considered as part of the design process.
 