My testers fine, batteries fully charged, and checked readings on my spare meter, exactly the same so the readings are correct, i think the ring is interconnected very close to the board and is duffing the reading up hence the 0.00 which is obviously not a correct/compliant reading as it suggests no resistance............there must be a reason for it

Ok if you think the ring is interconnected close to the board why did you not open a socket at the half way point and test there. I would suspect ring leaving board probably straight to a JB then on to sockets.
 
Seen readings like this once - the CU had been moved down the wall and the offending JB was under the floor board - the sparky had connected 4 cables into one 30A jb!
 