I

irishsailor

Can anyone shed a little light on this please

How is the cable factors worked out on a ring??

32A Circuit breaker 2.5 T&E clipped direct 27A

How is the calc worked out for the above as I wa on the understanding that the cable capacity has to be greater than the Fuse rating??

Can you please explain

Irish
 
Hi mate,

If it was a 2.5 t&e radial the capacity would be 27A and you would use
a 20A breaker.

Being a ring, the current carrying capacity is higher (not sure how much-haven't got
my regs on me) - but its more than 32 A.

Hope that helps,

Cheers,

Wayne
 
Hi mate,

If it was a 2.5 t&e radial the capacity would be 27A and you would use
a 20A breaker.

Being a ring, the current carrying capacity is higher (not sure how much-haven't got
my regs on me) - but its more than 32 A.

Hope that helps,

Cheers,

Wayne


It is because you have 2 x 2.5mm T&E in parallel that is why you can use a 32A breaker on a ring circuit.
 
general domestic premises there should be a separate ring

Final circuit for every 100mm2 of floor area. must remember
That the maximum load that can be connected to a ring protected
By a 30A / 32A fuse is just over 7 kW, and the number of circuits Selected accordingly

rule of thumb


( 433.1.5 p : 74

Ring final circuit volt drop
Ring final circuit : ( cable doubled )

<<< Cable length to farthest point >>>
is ½ ( cable length )
2.5mm2 Line conductor :
1.5mm2 Protective conductor :

to the farthest point in effect two cables are run , so ( mV / A / m ) is halved and the length
of doubled cable to the farthest point is half the length of cable in the ring , given a multiplier of ( 4 )

the design current ( Ib ) in each leg of the cable is not to exceed 20A ,
for ring circuits the equation becomes :


Multiplier
4 x 11.5 x 1000
Lvd = -------------------------------------- for ring circuits
Ib x ( mV / A / m ) x Ct

Ring final circuit wired with 2.5mm2 regs : 4D5 , p: 282 ( mV / A / m ) = 18

mV / A / mand assumingIbis 32A and Ct is 1 then
*
( The maximum circuit length is then the smallest of 2 ) to 4 )
Multiplier5% amp mV meters
Lvd = 4 x 11.5 x 1000 / 32 / 18 = 79.9 m
*
Multiplier
Answer 4 x 11.5 x 1000 div 32 div 18 = 79.9 m
Answer 2 x 11.5 x 1000 div 32 div 18 = 39.9 m

However , in a ring circuit the current in a ring will not be the same all round the ring .
If it is assumed to be 20A at the far end and additional 12A is evenly distributed ,
The average current is ( 32A + 20 ) / 2 = 26A , and
Answer ( 32 + 20 = 52 div 2 = 26amp


Multiplier5% amp mV meters
Lvd = 4 x 11.5 x 1000 / 26 / 18 = 98.3 m
*

If Ct is to be calculated assuming Cg is 1 , cable Ib is 26 / 2 , conductors It is 20 and tp is 70oC ,
Then Ct = 0.923 and Lvd = 106.5m
 
Last edited by a moderator:

Reply to Ring Main Help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can someone explain electrically why we can spur unfused from a ring final on a 32a breaker when the cable is 2.5mm rated at max 27a?
Replies
4
Views
908
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hi all, I'm planning to remove a stud wall seperating my dining room and kitchen. On the dining room side of the stud wall, there is a double...
Replies
1
Views
945
Client currently has a DB in his outhouse. It feeds a pool pump and an air source heat pump. It is currently being supplied using a 4mm T&E cable...
Replies
9
Views
601
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock