Ring r1 issue.

All three scenarios, one end, other end, both ends:

1626723984422.png
 
OK mate, im going in tomorrow, disconnected one side of the ring, im going round. Will the whole ring be enigeresed if there's no fault. If there's a fault some of the ring won't work.
It'll still be live with a broken leg because it's still fed from both sides. Just break it into smaller sections and carry out your dead tests. Once you have confirmed what it is, if you can repair it or replace damaged leg all well. If not last resort is 2 radials.
 
It isn't necessarily strange as the break maybe between the board and first socket. Making one leg of the circuit live to find this fault is poor advice, the best advice is dead continuity tests as previously stated. The circuit may only have a high resistance joint and not a clean break hence the method you tried indicated they are all live, you are a trainee and this was inappropriate advice. A continuity tester may well show open circuit which may mean clean break or a high resistance connection which is above the range your tester it set to. Try an insulation resistance test across the two ends and see if it is clearly open. Either way you need to do cold continuity tests to find the fault.
 
It isn't necessarily strange as the break maybe between the board and first socket. Making one leg of the circuit live to find this fault is poor advice, the best advice is dead continuity tests as previously stated. The circuit may only have a high resistance joint and not a clean break hence the method you tried indicated they are all live, you are a trainee and this was inappropriate advice. A continuity tester may well show open circuit which may mean clean break or a high resistance connection which is above the range your tester it set to. Try an insulation resistance test across the two ends and see if it is clearly open. Either way you need to do cold continuity tests to find the fault.
I've linked r1 and rn at the board. I'm get around 0.65 at every socket, except one, it's high 1.2 it a spur.
 
I've linked r1 and rn at the board. I'm get around 0.65 at every socket, except one, it's high 1.2 it a spur.
Is this the figure-of-eight test?

If it look like there is no longer a break in the ring then either it was due to moving the connections at the MCB end (but I would expect you would have noticed a poor clamp, or it gripping the insulation and not wire), or somehow testing with 230V on one leg but not the other has blown away some thin corrosion somewhere and contact is made once more.

That is actually the worst possible outcome as the fault is still present, just no longer showing up on test :(
 
This is the problem with testing "by the book". The mot important thing when dealing with what may be an intermittent fault is to disturb absolutely NOTHING more than you can help, before you have a good indication of where the fault may be located.
Disconnecting one leg at the MCB and then going around the property with a Voltstick would have disturbed nothing more than the readily accessible and observable at the MCB.
 
Have you redone a continuity test at the ends including an IR test across them.
 
Give the test leads a good squeeze and make sure it's really 5 ohms.
My suspicion is that the loose connection is one you have already touched.
I also suspect you may have linked r1 and rn on opposite legs earlier.

Don't do any more live tests until the dead tests make sense.
 