Currently reading:
Ring r1 issue.
Discuss Ring r1 issue. in the UK Electrical Forum area at ElectriciansForums.net
Iona222
Trainee
I've volunteer to do some fault finding tomorrow on ring circuit. r1 no continuity.
I'm going to use the long lead method. Try work out if the r1 is broken, if it broken I need to blank off the socket and turn it into 2 radials. I need to buy 2 x 20amp breakers. Anything else I should look for, or any advice. Cheers.
The two 20A radials is always an option, but if the location of the break is such that the two legs are radically different lengths, I would perhaps be focusing on fixing the problem, particularly if the circuit serves a high usage location like a kitchen.
In terms of blanking off... I would try not to remove any accessories from service... if the break is on a cable leg from one place to another, just get yourself some slim 4 way push fit Wagos and earth out the cables for that section at both ends.
In my experience, such issues have typically been caused by loose connections in the accessories themselves. Thankfully I've not had many that involved hidden junction boxes... but one of them sticks in my mind where I managed to get the location down to the wall behind a newly installed kitchen cupboard :)
If you don't fancy dragging the long lead around you could also just link our line and neutral on one end of the cable and then go around taking an R1+R2 reading until it goes to the dogs... then do the same but with the other leg linked out. Draw a diagram and record the results... can help working out potential cable routes and may also highlight whether you are looking for multiple issues.
Good luck :)
Good luck :)
I try this thanks for the reply.
Very good advice above. The advantage of linking out one end and testing, then the other end and testing is you also find the rough route of the wiring as you go without having to dismantle dismantling lots of things.
Usually the problem is between the two highest readings in each direction. A spur can confuse things though, so if you find one of them is a spur ignore that socket completely as if it isn't there.
Before you start I'd check end-to-end rn and r2 for yourself and check these values look sane.
(If you have a break or poor connection in r2 at a different point then it can royally confuse things!)
All the best with it. It's very satisfying when you find and fix one of these!
Disconnect one live for the RFC at the consumer. Put the cover on and switch back on, the go around the property with a Voltstick, or even a table lamp, until you find where it ceases to work.
Should give you a good idea of where to start looking for the actual break.
Have used that method as well :)
Just make sure the disconnected end is made safe…..
last thing you need is a floating wire suddenly going live
By connecting each end in turn it can help find the break:
OK mate, im going in tomorrow, disconnected one side of the ring, im going round. Will the whole ring be enigeresed if there's no fault. If there's a fault some of the ring won't work.
You were too quick for me, I tried to edit that comment as I realised I'd missed your point.
See diagrams I replaced the comment with. I think you get it now.
Basically some will work depending on which end you connect. The important thing is not to leave the other end loose in the consumer unit, stick a wago on it.
It'll still be live with a broken leg because it's still fed from both sides. Just break it into smaller sections and carry out your dead tests. Once you have confirmed what it is, if you can repair it or replace damaged leg all well. If not last resort is 2 radials.
It isn't necessarily strange as the break maybe between the board and first socket. Making one leg of the circuit live to find this fault is poor advice, the best advice is dead continuity tests as previously stated. The circuit may only have a high resistance joint and not a clean break hence the method you tried indicated they are all live, you are a trainee and this was inappropriate advice. A continuity tester may well show open circuit which may mean clean break or a high resistance connection which is above the range your tester it set to. Try an insulation resistance test across the two ends and see if it is clearly open. Either way you need to do cold continuity tests to find the fault.
I've linked r1 and rn at the board. I'm get around 0.65 at every socket, except one, it's high 1.2 it a spur.
Is this the figure-of-eight test?
If it look like there is no longer a break in the ring then either it was due to moving the connections at the MCB end (but I would expect you would have noticed a poor clamp, or it gripping the insulation and not wire), or somehow testing with 230V on one leg but not the other has blown away some thin corrosion somewhere and contact is made once more.
That is actually the worst possible outcome as the fault is still present, just no longer showing up on test :(
This is the problem with testing "by the book". The mot important thing when dealing with what may be an intermittent fault is to disturb absolutely NOTHING more than you can help, before you have a good indication of where the fault may be located.
Disconnecting one leg at the MCB and then going around the property with a Voltstick would have disturbed nothing more than the readily accessible and observable at the MCB.
I've changed a couple of circuits and I'm getting 5.01 ohms on r1. Least I'm getting continuity.
Have you redone a continuity test at the ends including an IR test across them.
I'm getting 0.55 on rn. 4.5 on r1. I.r. Live to live 500M
Give the test leads a good squeeze and make sure it's really 5 ohms.
My suspicion is that the loose connection is one you have already touched.
I also suspect you may have linked r1 and rn on opposite legs earlier.
Don't do any more live tests until the dead tests make sense.
Reply to Ring r1 issue. in the UK Electrical Forum area at ElectriciansForums.net