I've volunteer to do some fault finding tomorrow on ring circuit. r1 no continuity.

I'm going to use the long lead method. Try work out if the r1 is broken, if it broken I need to blank off the socket and turn it into 2 radials. I need to buy 2 x 20amp breakers. Anything else I should look for, or any advice. Cheers.
 
The two 20A radials is always an option, but if the location of the break is such that the two legs are radically different lengths, I would perhaps be focusing on fixing the problem, particularly if the circuit serves a high usage location like a kitchen.

In terms of blanking off... I would try not to remove any accessories from service... if the break is on a cable leg from one place to another, just get yourself some slim 4 way push fit Wagos and earth out the cables for that section at both ends.

In my experience, such issues have typically been caused by loose connections in the accessories themselves. Thankfully I've not had many that involved hidden junction boxes... but one of them sticks in my mind where I managed to get the location down to the wall behind a newly installed kitchen cupboard :)

If you don't fancy dragging the long lead around you could also just link our line and neutral on one end of the cable and then go around taking an R1+R2 reading until it goes to the dogs... then do the same but with the other leg linked out. Draw a diagram and record the results... can help working out potential cable routes and may also highlight whether you are looking for multiple issues.

Good luck :)
 
The two 20A radials is always an option, but if the location of the break is such that the two legs are radically different lengths, I would perhaps be focusing on fixing the problem, particularly if the circuit serves a high usage location like a kitchen.

In terms of blanking off... I would try not to remove any accessories from service... if the break is on a cable leg from one place to another, just get yourself some slim 4 way push fit Wagos and earth out the cables for that section at both ends.

In my experience, such issues have typically been caused by loose connections in the accessories themselves. Thankfully I've not had many that involved hidden junction boxes... but one of them sticks in my mind where I managed to get the location down to the wall behind a newly installed kitchen cupboard :)

If you don't fancy dragging the long lead around you could also just link our line and neutral on one end of the cable and then go around taking an R1+R2 reading until it goes to the dogs... then do the same but with the other leg linked out. Draw a diagram and record the results... can help working out potential cable routes and may also highlight whether you are looking for multiple issues.

Good luck :)
I try this thanks for the reply.
 
Very good advice above. The advantage of linking out one end and testing, then the other end and testing is you also find the rough route of the wiring as you go without having to dismantle dismantling lots of things.
Usually the problem is between the two highest readings in each direction. A spur can confuse things though, so if you find one of them is a spur ignore that socket completely as if it isn't there.

Before you start I'd check end-to-end rn and r2 for yourself and check these values look sane.
(If you have a break or poor connection in r2 at a different point then it can royally confuse things!)

All the best with it. It's very satisfying when you find and fix one of these!
 
Disconnect one live for the RFC at the consumer. Put the cover on and switch back on, the go around the property with a Voltstick, or even a table lamp, until you find where it ceases to work.
Should give you a good idea of where to start looking for the actual break.

Have used that method as well :)
 
Disconnect one live for the RFC at the consumer. Put the cover on and switch back on, the go around the property with a Voltstick, or even a table lamp, until you find where it ceases to work.
Should give you a good idea of where to start looking for the actual break.
Just make sure the disconnected end is made safe…..

last thing you need is a floating wire suddenly going live
 
Disconnect one live for the RFC at the consumer. Put the cover on and switch back on, the go around the property with a Voltstick, or even a table lamp, until you find where it ceases to work.
Should give you a good idea of where to start looking for the actual break.
Would half the circuit not be working anyway? With half ring disconnected?
 
By connecting each end in turn it can help find the break:
1626723469899.png
 
Last edited:
If you connected two radial circuits to the same MCB (forget the regs a minute) would they both work?
OK mate, im going in tomorrow, disconnected one side of the ring, im going round. Will the whole ring be enigeresed if there's no fault. If there's a fault some of the ring won't work.
 
OK mate, im going in tomorrow, disconnected one side of the ring, im going round. Will the whole ring be enigeresed if there's no fault. If there's a fault some of the ring won't work.
You were too quick for me, I tried to edit that comment as I realised I'd missed your point.
See diagrams I replaced the comment with. I think you get it now.
Basically some will work depending on which end you connect. The important thing is not to leave the other end loose in the consumer unit, stick a wago on it.
 
OK mate, im going in tomorrow, disconnected one side of the ring, im going round. Will the whole ring be enigeresed if there's no fault. If there's a fault some of the ring won't work.
It'll still be live with a broken leg because it's still fed from both sides. Just break it into smaller sections and carry out your dead tests. Once you have confirmed what it is, if you can repair it or replace damaged leg all well. If not last resort is 2 radials.
 

Reply to Ring r1 issue. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hope you're all well . I've had ring door bell 2nd generation hardwired for 1.5 yrs... it was connected to transformer which is connected to the...
Replies
22
Views
1K
Hey there, Sorry I’ve just joined up. I’m a qualified electrician/Electrical engineer. Recently sat my 2391-52. My question is I had a fault...
Replies
4
Views
1K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
178
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock