I've changed a couple of circuits and I'm getting 5.01 ohms on r1. Least I'm getting continuity.

I'm getting 0.55 on rn. 4.5 on r1. I.r. Live to live 500M
At least it is still present to be found.

Try linking L & N at one end (L & N open on other leg) and go round checking low ohm resistance L-N at each socket, it should be low-ish (0-1 ohm or so) on that side until you get to around the fault and then probably 4 ohm is added.

Then do the opposite (link L-N other leg, open first leg) and see if you find the fault at the same socket.
 
Then do the opposite (link L-N other leg, open first leg) and see if you find the fault at the same socket.
Just to correct that, you probably will find two sockets where there is a change when checked from both direction. Assuming just the one fault (hmm, yes...) then it will be the link between them that has the high R problem.

If lucky and there is no stupid hidden junction box then probably one of those sockets will be found to have a poor connection / loose screw and correcting that ought to result in r1 & rn being practically identical.
 
Just to correct that, you probably will find two sockets where there is a change when checked from both direction. Assuming just the one fault (hmm, yes...) then it will be the link between them that has the high R problem.

If lucky and there is no stupid hidden junction box then probably one of those sockets will be found to have a poor connection / loose screw and correcting that ought to result in r1 & rn being practically identical.
Gave up on it, whet round all the sockets. There's a loft but no access. High, fluctuating r1 reading. Least I got it improved from no continuity. My friend just bought the house was good experience like, but wish I was successful on resolving the issue.
 
Open circuit is relatively safe. An open circuit passes no current, so develops no heat.
A resistive joint, like you have now, produces heat in watts to the product of the current flowing through it and the resistance of the fault.
Much more dangerous than it was.
 
You need to advise your friend to have this looked at or have another go with a clear mind.
 
Not give up?
I've followed all the advise, he needs to get someone with more experience. If you fancy a drive to Glasgow?.. I didn't get access to the loft to check for cables damaged or so. I could change the rest of the sockets I didn't change. Or than that.
 
I've followed all the advise, he needs to get someone with more experience. If you fancy a drive to Glasgow?.. I didn't get access to the loft to check for cables damaged or so. I could change the rest of the sockets I didn't change. Or than that.
Don't give up on the fault. If you can't fault find you'll never be a good spark and many out there can't. Persevere and it'll be worth it there's nothing like hands on experience to learn. I've been there and it's ---- having to do it yourself at the start but you'll be glad you did.
 
Don't give up on the fault. If you can't fault find you'll never be a good spark and many out there can't. Persevere and it'll be worth it there's nothing like hands on experience to learn. I've been there and it's ---- having to do it yourself at the start but you'll be glad you did.

^This.

Numerous experiences of sparks who walked away, when things weren't straightforward enough for their liking, left me with a very poor impression of the trade for many years. It's also what has driven me to retrain.
 
I recall some good advice I was given by an irritatingly good elderly sparks - "if you can find the issue, find something that does work, no matter how simple, and build on it.".
In this case just proving that r1+r2 to the first socket on each leg (with the end linked) is a sensible number would be a fantastic start and boost your morale as you then know you will find the problem in the end. Even if it means testing each length of cable individually! It isn't the most efficient way but if it works, who cares!
 
I've followed all the advise, he needs to get someone with more experience. If you fancy a drive to Glasgow?.. I didn't get access to the loft to check for cables damaged or so. I could change the rest of the sockets I didn't change. Or than that.
Take a short break and then go back. you will never gain the skills you need if you don't keep trying!

Taking a systematic and logical approach is essential or you will be chasing your own imagined tail. You might have more than one fault, you might have a fault in a hidden junction box, but if you apply some of the suggested tests you should be able to pin down the two sockets where there is an unacceptably high r1 between them.

At that point you have a couple of courses of action.

You can double-check that the two socket connections are fine, at which point you know there is a "cable" fault. It might be the hidden fault is feeding a spur, so if you isolate both good ends (so sockets 1...A are all good one one leg, and C...N are good on the other leg, but B is now open - its a spur off a junction box).

The locations of them might give you a clue as to what is up.

Maybe the junction feeds something you have not found (e.g. aerial amplifier in loft?)

If you find both isolated legs are moderately similar numbers of sockets and no other problems then you might call it quits and put them on two 20A MCB/RCBOs as radials and be done (after checking the Zs values...)

Imagine the RFC, now think of a section as bad and think "How can I find it by measurement along?"
 
Don't give up on the fault. If you can't fault find you'll never be a good spark and many out there can't. Persevere and it'll be worth it there's nothing like hands on experience to learn. I've been there and it's ---- having to do it yourself at the start but you'll be glad you did.
I agree with all that mate. Im not going back the tenant was hassling me all day. Secondly other than get a key to check the loft what else can I do, I took off a sockets changed 4, followed the advise on this I.r test was 500M life to live. Im moving on. Thanks for all the advise.
 
The characteristics of the fault seem to have changed since you started investigating it, so it's your baby now. You can't just walk away knowing the installation is potentially dangerous.
Tenant doesn't get any say in the matter. I'm sure the tenancy agreement covers access for essential maintenance.
 