Dont give up.. Try this...
Go back to basics, you know rn and r2 are good right?
So disconnect all conductors and seperate at the CU... Then remove all sockets (Every single one) and disconnect and seperate all conductors.
Now go back to the consumer unit, choose one of the two legs, connect rn and r2 together, now go round each socket with a continuity tester testing each cable between neutral and cpc.
When you get continuity you know thats your first socket (Continue to check all sockets incase of hidden JB's) so it goes from the cu to that socket, now at the cu connect r1 and r2, go back to that socket and test continuity between live and cpc, if you have continuity the connect that cable to another cable in that socket, (If there are only two cables then you can put that socket back on).
Go back to the cu and change back to connected rn and r2, now follow same as above and go find your second socket, if there are more than two cables you will either find a spur in which case go back to your first socket and connect your known good cable to the other cable, or you will find the next socket in the ring. when you have found the next socket again go back to cu and connect r1 and r2 and check at second socket...
Eventually you will find where the break is between two sockets, Once you have found the issue you can next think about how best to fix it. Its not quick but at least you will find it..
Remember you dont know where the cables are run so trying to do things by the book such as splitting the ring in half does not always work. Keep it simple by disconnecting it all at the CU and thinking of it as a radial.
Hope the above made sense and helps. Good luck..