The manual for my heater states "wire from controller to heater needs to be UL62 approved to 105C". I found SJEEOW wire on McMaster Carr. Can buy a 10-foot piece for $22.

My question is: Does NEC allow SJEEOW to be placed in studs in wall (similar to Romex)?
The answer is no, you need to buy 6/3 with ground that’s approved for outdoor use. The insulation for SJEEOW and it’s not good for 60 amps.
 
The answer is no, you need to buy 6/3 with ground that’s approved for outdoor use. The insulation for SJEEOW and it’s not good for 60 amps.
I didn't specify... my heater is 6.5 kW (240VAC), so about ~27 amps.
 
All your wire needs to be # 6. Your manual actually states 60 amps. Do not use short cuts on cheap wire. Especially any kind of SO cable
No short cuts here. My manual states 10 Ga wire rated to 105C. The wire I bought is 10 Ga and rated to 105C.

My question is: Can I run SJEEOW in the wall? An electrician I called (before I got the SJEEOW), said "Only Romex in wall, has to be insulated".
 

Attachments

  • Heater.PNG
    Heater.PNG
    43.2 KB · Views: 48
Last edited by a moderator:
No short cuts here. My manual states 10 Ga wire rated to 105C. The wire I bought is 10 Ga and rated to 105C.

My question is: Can I run SJEEOW in the wall? An electrician I called (before I got the SJEEOW), said "Only Romex in wall, has to be insulated".
Article 400.12 states it is not permitted to run through holes in walls. It will handle 30 amps and it’s not approved for wet locations
 
Great. Then I run it in metal conduit inside the wall? Not a wet location so I'm good there.

Can you explain why you were insistent on 6 GA?
 
Great. Then I run it in metal conduit inside the wall? Not a wet location so I'm good there.

Can you explain why you were insistent on 6 GA?
Every hot tub or SPA I’ve wired called for a 50 or 60 amp GFCI breaker and I usually go with #6 which I keep in stock in my truck
 
Every hot tub or SPA I’ve wired called for a 50 or 60 amp GFCI breaker and I usually go with #6 which I keep in stock in my truck
Thanks, that makes sense for that current load.

What about running SJEEOW in metal conduit through the studs? Will the inspector freak out?
 
No he won’t flip out but why metal and not PVC conduit
That's a good question... I bought flexible metal already! Can probably return that and go with cheaper PVC.... in fact I probably have a 3 foot chunk in the office that I can use. Looking for a deep feedthrough to go through the 5/8" cedar, will probably have to put a metal plate there?
 
That's a good question... I bought flexible metal already! Can probably return that and go with cheaper PVC.... in fact I probably have a 3 foot chunk in the office that I can use. Looking for a deep feedthrough to go through the 5/8" cedar, will probably have to put a metal plate there?
Yes every stud you drill through you have to install a nail plate which you can purchase at Home Depot and Lowe’s or your local electrical parts house. Good luck
 