Discuss SD Q1TF bad hammer in breaker? in the UK Electrical Forum area at ElectriciansForums.net
Badger
40 year old square D QF1TF long span top fed.
I turned off 30 amp double pole to water heater and still had a closed circuit, then turned off the main above.
I then returned to reconnect service at main on service panel only to find that I now was experiencing voltage drop on outlets in home. EX: toaster on would drop voltage to appro 60-70 volts.
This is not over entire house but on some circuits.
Tested phase to phase at incoming = 220v
Leg to ground =110v on singles
30 amp double = 110v each but 0 ACROSS.
Neutral to ground = 0
Do I have a bad leg on main from bad contact on the hammers in breaker ? OR a neutral issue.
I also replaced all outlets in entire house.
This is a 1974 skyline mobile home with copper wire throughout
Thanks in advance.
Thanks in advance.
You have a neutral issue if your reading if you are getting that low of voltage. One of the outlets that you changed has a bad connection with a loose neutral. Probably just on 1 circuit
This happened after I turned off 100amp main, not after I did the receptacles.Things were fine before.
The Breaker is over 40 years old and is discontinued. Sd Q1tf top feed. I have lost the neutral on one leg at the breaker is my best guess.
Then I suggest that you upgrade your main panel to a safer 200 amp panel. Good luck with your project
Reply to SD Q1TF bad hammer in breaker? in the UK Electrical Forum area at ElectriciansForums.net
I would like to ask advice on a breaker size. Back in 2001 I turned my garage into a woodworking shop with several 240v machines. To power them I...
Hi All, I have a 1950s rental house with a 100 amp main panel with a main shut off breaker. Breakers are Eaton/Cutler Hammer type, so the...
Summary (TL;DR) Several lightbulbs in my home supplied by one circuit breaker dim over time and go out in about a year. Right now, the ceiling...
I have a Single Phase Power box for a townhouse. When I read voltage across the Hot legs (A) and (B) to ground I get 123 volts with the main...
Hi All, I am new to the forum. I have a small 30 amp sub panel that once powered a green house, some lights and 1 regular 120-v outlet. We...