Discuss SD Q1TF bad hammer in breaker? in the Electrical Forum area at ElectriciansForums.net

Welcome to ElectriciansForums.net - The American Electrical Advice Forum
Head straight to the main forums to chat by click here:   American Electrical Advice Forum

Badger

DIY
Reaction score
0
40 year old square D QF1TF long span top fed.
I turned off 30 amp double pole to water heater and still had a closed circuit, then turned off the main above.
I then returned to reconnect service at main on service panel only to find that I now was experiencing voltage drop on outlets in home. EX: toaster on would drop voltage to appro 60-70 volts.
This is not over entire house but on some circuits.
Tested phase to phase at incoming = 220v
Leg to ground =110v on singles
30 amp double = 110v each but 0 ACROSS.
Neutral to ground = 0
Do I have a bad leg on main from bad contact on the hammers in breaker ? OR a neutral issue.
I also replaced all outlets in entire house.
This is a 1974 skyline mobile home with copper wire throughout
Thanks in advance.
 
40 year old square D QF1TF long span top fed.
I turned off 30 amp double pole to water heater and still had a closed circuit, then turned off the main above.
I then returned to reconnect service at main on service panel only to find that I now was experiencing voltage drop on outlets in home. EX: toaster on would drop voltage to appro 60-70 volts.
This is not over entire house but on some circuits.
Tested phase to phase at incoming = 220v
Leg to ground =110v on singles
30 amp double = 110v each but 0 ACROSS.
Neutral to ground = 0
Do I have a bad leg on main from bad contact on the hammers in breaker ? OR a neutral issue.
I also replaced all outlets in entire house.
This is a 1974 skyline mobile home with copper wire throughout
Thanks in advance.
You have a neutral issue if your reading if you are getting that low of voltage. One of the outlets that you changed has a bad connection with a loose neutral. Probably just on 1 circuit
 
You have a neutral issue if your reading if you are getting that low of voltage. One of the outlets that you changed has a bad connection with a loose neutral. Probably just on 1 circuit
This happened after I turned off 100amp main, not after I did the receptacles.Things were fine before.
The Breaker is over 40 years old and is discontinued. Sd Q1tf top feed. I have lost the neutral on one leg at the breaker is my best guess.
 
This happened after I turned off 100amp main, not after I did the receptacles.Things were fine before.
The Breaker is over 40 years old and is discontinued. Sd Q1tf top feed. I have lost the neutral on one leg at the breaker is my best guess.
Then I suggest that you upgrade your main panel to a safer 200 amp panel. Good luck with your project
 

Reply to SD Q1TF bad hammer in breaker? in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.