R

Rededdie

I have a Single Phase Power box for a townhouse. When I read voltage across the Hot legs (A) and (B) to ground I get 123 volts with the main breaker turned off. With all the circuit breakers turned off and powering up the main breaker to the panel I still have 123 volts across both (A) and (B). As I start to turn on the branch circuit breakers on to each Outlet, Light, Garbage Disposal, Washer etc..... The voltage changes but it ranges from (A) -- 134volts, (B)--- 104volts, as i keep going down the panel turning circuits on the voltage changes and never evens out back to (A) 123volts, (B) 123volts, or anywhere close to it. The worst I have seen on this panel is (A) -- 154volts, (B) -- 94volts. The panel did not have a ground on it from the ground rod which I corrected and tied it into the ground strip and Jumper'd over to the neutral bar.

Everything I have read about this issue is that it is a neutral problem and I thought it was a floating neutral at one time but had the feeling it has always been a neutral issue. But as I have researched this I have come to understand that it is more than likely the PoCo that has a broken neutral going to this panel on their end not on my end... Is this correct.? Is there another issue I should be looking at.?

Any assistance would be greatly appreciated. Thanks
 
I have a Single Phase Power box for a townhouse. When I read voltage across the Hot legs (A) and (B) to ground I get 123 volts with the main breaker turned off. With all the circuit breakers turned off and powering up the main breaker to the panel I still have 123 volts across both (A) and (B). As I start to turn on the branch circuit breakers on to each Outlet, Light, Garbage Disposal, Washer etc..... The voltage changes but it ranges from (A) -- 134volts, (B)--- 104volts, as i keep going down the panel turning circuits on the voltage changes and never evens out back to (A) 123volts, (B) 123volts, or anywhere close to it. The worst I have seen on this panel is (A) -- 154volts, (B) -- 94volts. The panel did not have a ground on it from the ground rod which I corrected and tied it into the ground strip and Jumper'd over to the neutral bar.

Everything I have read about this issue is that it is a neutral problem and I thought it was a floating neutral at one time but had the feeling it has always been a neutral issue. But as I have researched this I have come to understand that it is more than likely the PoCo that has a broken neutral going to this panel on their end not on my end... Is this correct.? Is there another issue I should be looking at.?

Any assistance would be greatly appreciated. Thanks
My friend you are correct about your readings on your voltage and it is definitely a neutral issue. 154vac is way to high and can burn up appliance’s, clocks, microwave etc. other than calling the power company check the voltage on the actual wires coming from the meter. It could easily be on the power company’s side
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Power Panel Changes Voltage with Branch Circuits
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
Rededdie,
Last reply from
Megawatt,
Replies
1
Views
1,242

Advert