Hi everyone,

I need some help with an electrical issue I'm experiencing. I recently created a new circuit for an electric oven at my friend's place, and when I returned home, my friend called to say that the two water pipes connected to the boiler were smoking.

When I arrived, I first measured that there was no voltage in the supply line feeding the boiler (it's on a separate circuit controlled remotely from the rest of the house). However, I measured a voltage of 110V between the neutral wire of the boiler and the water pipes (we use 230V single phase in Hungary, and the pipes are made of iron). I also measured a slight difference in voltage between the two water pipes, which could have caused an arc between them.

Here's what's happening: when the oven is turned on and operated at its maximum load, I measure 110-115V between the water and the neutral wire. However, if only a part of the oven is turned on at a lower load, I only measure 30-35V between them. It's worth noting that the wiring in the house is old and the connections in the distribution box are just twisted together. All of the neutral wires (I counted five) are also twisted, and I didn't undo them. Instead, I cut one of the neutral wires and connected it to a terminal block with the neutral wire of the oven cable.

Tomorrow, after work, I plan to replace the twisted connections of the neutral wires. However, if the problem persists, I'm not sure what to do next. The house has three-phase wiring (one phase is used for the whole house, one for the oven, and one is unused), as well as a neutral wire. The neutral wire is not separated onto a separate protective ground in the meter box, unfortunately, and I can't touch the meter box since only the utility's authorized technician can do that.

I'm afraid I may have done something wrong, so any ideas or suggestions would be greatly appreciated. Thank you!
 
first thing to do is turn off the power to the house,
swallow your pride and get someone who is knowledgeable in electrics to come look at it.

what you have is dangerous and needs more than a bit of internet advice, it needs a hands on approach from a professional.

sorry to be harsh but if you are seeing smoke from pipes and measuring voltages more than a couple of volts between pipes and Neutral or earth, you have a serious problem that could be fatal.
 
The neutral wire is not separated onto a separate protective ground in the meter box,

This is important. On a TN-C system with a combined neutral / protective earth, a broken / high resistance conductor or connection can cause exposed metalwork to become live. You then have the question: What is live? The pipes with respect to the (earthed) neutral conductor, or the neutral conductor with respect to the (earthed) pipes. With TN-C, one false move and you can create a death-trap. Large single-phase loads will show problems up to the greatest extent by creating the highest neutral current.

I appreciate that any problem with the combined neutral / earth is probably not of your making, but as above you would do well not to take on any responsibility for it unless you are fully competent and qualified. It's a much riskier scenario than wiring in an oven to an otherwise intact system.

I would be interested to see pics. Something might be obvious.
 
You wonder if this issue was there before the additional circuit was added….

Will it be 3ph like UK? Ie 400v between phases and 230 ph-n or is the 110 the expected full voltage
 
Will it be 3ph like UK? Ie 400v between phases and 230 ph-n

Yes, 230/400V throughout. I don't know whether they ever used 230V delta or whether any is still in use today, but that obviously doesn't apply here.
 

Reply to How can there be voltage on water pipes? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
262
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
568
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
770
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
I'm not sure what's going on with my kitchen light. I've replaced an old 28W CFL fitting with a new 4 x LED GU10 fitting (a cheap one from...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock