Discuss Secondary Switchboard for kitchen from Primary Switchboard in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Probably made in china........

I think one of these is called for here :D

saucer-of-milk.jpg
 
Radials are safe and have thier place in the uk.
rings are also safe and also have thier place in the uk.

the idea of running a sub main to a second CU in domestic setting is admirable but over complicating a simple job, you should not use circuit breakers as switching for your appliances, firstly they are not intended to be used for regular on off actions, this could cause wear and ultimately failure.

the 10mm cable can carry 64a, BUT that's makes 2 assumptions,
first
its flat twin and earth
second
its clipped directly to the wall, without being enclosed or covered with insulation.

so with those 2 assumptions satisfied yeah you could potentially upgrade to a 63a mcb/Rcd combination, but they are not likely to be satisfied, as you don't want anything on show, so worst case scenario is the cable can only carry 32a.

when you had an electrician on site and he advised you, he is the best person to listen to, for all the advice we have given has been given on the information YOU have supplied, but with your limited( and that's being kind) knowledge of bs 7671, you may have left out some very valuable information, like the construction of the building, or that your 17th century mansion has its own power station which runs on 110v.

get an electrician in, tell him what you want including some central controls, then let HIM tell YOU the best way of doing it, not the other way round. Laws and regulations need to be satisfied before any consideration of your aesthetic opinion.
 
but don't get the spark who advised that you need a separate MCB for each socket outlet. he's got less knowledge of electrics than i have of piloting a helicopter.
 
the idea of running a sub main to a second CU in domestic setting is admirable but over complicating a simple job, you should not use circuit breakers as switching for your appliances, firstly they are not intended to be used for regular on off actions, this could cause wear and ultimately failure.

There's nothing admirable about running a sub-main to a separate CU, for a typical run of the mill domestic kitchen!! If the house was the size of a mansion, that would may be another matter!!

This guy is a total idiot, and isn't going to listen to anyone. Best leave him to his own devices!!
 

Reply to Secondary Switchboard for kitchen from Primary Switchboard in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Great to of found this forum. Much respect for keeping everyone safe! My background is in commercial data and Audio Visual. Been...
Replies
0
Views
578
Hi all. So I'm designing my new kitchen and trying to plan where things will go. I currently have a 6 switch panel for the appliances (hob...
Replies
18
Views
1K
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
1K
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
1K
Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
594

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock