Seems the Schneider option would be suitable, such as:

It is wider, so that nasty enclosure and related stuff would need to be changed, and ideally a switch-fuse put in for over current and then the RED auto-recloser to avoid the need for cable replacement, so a bit of space juggling, but it would address the selectivity issue to a large degree (or at least some of the annoyance factor).

In my opinion that still would not comply, it will not minimise disruption in the event of a fault.
Yes it will auto re-close in the event of a nuisance trip, but that doesn't avoid nuisance tripping in the first place, or leave any circuits live during a genuine fault.
 
In my opinion that still would not comply, it will not minimise disruption in the event of a fault.
Well in reduces it, but not eliminate it. But to some degree you can say the same about a split-RCD board as not complient due to the impact on multiple circuits of an RCD trip.

Still, it is up to someone else to decide if they want to improve matters and the cost they are willing to bear in order to do so.

The auto-reclose option is a lot cheaper than a new run in SAW and related redecoration, so someone else can decide what to do. Not having to leave the house to reset the MCB or RCD would be a major improvement in practical terms, having a 5 sec gap (or so, presumably depending on how it is configured) in power might be a trade off they are willing to accept.
 
Well in reduces it, but not eliminate it. But to some degree you can say the same about a split-RCD board as not complient due to the impact on multiple circuits of an RCD trip.

, having a 5 sec gap (or so, presumably depending on how it is configured) in power might be a trade off they are willing to accept.

I can say it, and I do say it, twin RCD boards don't comply in my opinion.

It's only a 5 second gap for a nuisance trip, it's not going to come back on if there is a fault.
 
I can say it, and I do say it, twin RCD boards don't comply in my opinion.
I agree in the sense that I would prefer to only see all-RCBO boards used, but the majority of opinion in the UK industry is split RCD boards are acceptable. After all, for most folk they sit for years without tripping.

It's only a 5 second gap for a nuisance trip, it's not going to come back on if there is a fault.
True, but for a fault at an end circuit the related house CU RCD will almost certainly have tripped, so at least the remainder of circuits would have power restored. Yes, there are fault cases that would not be covered (e.g. leak on non-RCD circuit, or on the feed cable) but with a simple fuse-fed SWA solution they would probably develop in to a MCB-tripping fault in the not too distant future.
 
Not sure why people think dual rcd boards are non compliant, other than regulation 314, as regulation 531.3.5.2 allows several circuits to be protected by the same device except to where particular restrictions for selectivity apply.
 
Just curious about the earthing here. Those more into regs can help. The 16mm T&E has a 6mm earth, when say the calc says 10mm is needed. If the CU has a 10mm earth to a water pipe at the far end will all be within spec?
 
Just curious about the earthing here. Those more into regs can help. The 16mm T&E has a 6mm earth, when say the calc says 10mm is needed. If the CU has a 10mm earth to a water pipe at the far end will all be within spec?
I’ve been thinking about this. The t&e is fed from a DB that has 16mm earth conductor correctly sized. This cable is feeding the DB/CU inside the premises . However the 6mm CPC of the cable is not an earth conductor so sizing relating to main earth do not apply . However does it need to be deemed a bonding conductor? If I can get the water and gas bonded where they enter the property in 10mm then it complies I think ?
 
However does it need to be deemed a bonding conductor? If I can get the water and gas bonded where they enter the property in 10mm then it complies I think ?
That sound right, if you can bond them at the entry point to the whole building the T&E sub-main CPC would never see the full current of a PME fault so should be fine.
 
That sound right, if you can bond them at the entry point to the whole building the T&E sub-main CPC would never see the full current of a PME fault so should be fine.
That means getting a 10mm earth cable from the CU to a water pipe, which may be at the other side of the building. So that means the 6mm earth conductor in the 16mm T&E will not take all the fault current load.

John Ward has a vid doing the calulation of the earthing conductor. I was suprised how small they can be. In this case the impedance will have to be measured or known. Smaller than taking the size from a provided table - the table is for ball park convenience, which says below 16mm the CPC needs to be the same size. But calculate, then you can get it lower. He does the calcs.

View: https://www.youtube.com/watch?v=odnUIWyC0oU
 
  • The CPC (circuit protective conductor) is all the CPC conductors of all circuits that together are joined to the main earthing terminal near the DNO's fuse, joining all exposed conductive parts.
  • The earth conductor connects to the DNO's earth or an earth rod from the main earth terminal.
  • The bonding conductors connect extrenuous metal parts (gas pipe & water pipe, steel frame of building, etc) to the main earth terminal.
That separates them. into logical divisions. Realistically, the term includes the CPC, earthing conductor and the equipotential bonding conductors.

In this case the 6mm 'earth' wire in the 16mm T&E looks to be an earth, not a CPC as they in this installation are after the CU all joined at te CU's earth bar. Because it is in a T&E cable does not automatically make it a CPC.
 
  • The CPC (circuit protective conductor) is all the CPC conductors of all circuits that together are joined to the main earthing terminal near the DNO's fuse, joining all exposed conductive parts.
  • The earth conductor connects to the DNO's earth or an earth rod from the main earth terminal.
  • The bonding conductors connect extrenuous metal parts (gas pipe & water pipe, steel frame of building, etc) to the main earth terminal.
That separates them. into logical divisions. Realistically, the term includes the CPC, earthing conductor and the equipotential bonding conductors.

In this case the 6mm 'earth' wire in the 16mm T&E looks to be an earth, not a CPC as they in this installation are after the CU all joined at te CU's earth bar. Because it is in a T&E cable does not automatically make it a CPC.

The protective conductor in the T+E is the circuit protective conductor of the distribution circuit which feeds the CU. This may, or may not also need to perform the function of a main bonding conductor.
 
The protective conductor in the T+E is the circuit protective conductor of the distribution circuit which feeds the CU. This may, or may not also need to perform the function of a main bonding conductor.

Hi Dave please clarify - under which circumstances would athe CPC need also perform the function of a bonding conductor given this arrangement? ? We are not “exporting” the PME earth to an outbuilding here this is all internal to the same property.
 
Hi Dave please clarify - under which circumstances would athe CPC need also perform the function of a bonding conductor given this arrangement? ? We are not “exporting” the PME earth to an outbuilding here this is all internal to the same property.
You never export a PME earth you merely utilise a cpc which is derived from a PME earthing.
 