EICR: I’ve come across 30mA RCD supplying a consumer unit via a 63A MCB and 16mm T&E. connected via an isolator to the cutout PME. (Ground floor, outside meter cab on wall)


The T&E is concealed up the stairwell behind /within plaster into a 1st floor flat above a shop and into the CU so effectively has 6mm main earth.

(see pic for the bodge of an install of the RCD which has been wired incorrectly but functions - what would you code that ! )


The CU is a dual 30mA split load affair. Therefore no selectivity and any earth fault will likely trip the whole supply, as it did on RCD test

In addition NO bonding to gas or water which is another matter but related of course

I see options as below sny

1. rewire submain cable with SWA or surface mount with T&E (costly/messy/unsightly either way)

2. Replace Supply RCD with switch fuse but this breaches requirement of 30mA RCD for concealed cable -

3. Accept the selectivity/nuisance factor but the RCD supplying T&E is in an outside meter box with a lid that actually needs a tool to open

4. replace Supply RCD with time delay 100 mA RCD which does not comply with concealed cable requirements

4. submit EICR and leave for someone else to resolve !BC64BD59-9A4F-4928-9050-8B69FDDAFE5A.jpeg
 
Last edited by a moderator:
Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members
As it stands you cannot remove the 30ma rcd as you remove the additional protection, fitting 100ma (s) rcd also removes the additional protection.
Submit the Report and worry about any remedial works if asked.
The cpc of the cable is also inadequate to support PME bonding.
 

bill01803

-
Arms
What are the water/gas mains made of?
 
  • Thread Starter Thread Starter
  • #4
What are the water/gas mains made of?
Copper. Gas is easy fix it’s in adjacent meter cab. Water not so easy - far end of flat. Suspect feed is from shop below. Need to talk to landlord on that. Might be an option to install a plastic section in water supply.
 
  • Thread Starter Thread Starter
  • #6
Is the water supply the same for the shop and flat?
Not sure mate I need to find out. All I know currently there are no bonding conductors in the flat CU or in the meter cabinet supply origin. 🤔
 

Strima

-
Arms
Esteemed
Not sure mate I need to find out. All I know currently there are no bonding conductors in the flat CU or in the meter cabinet supply origin. 🤔
If the flat and shop share water supplies then they could be bonded back to a common MET.

Are the flat and shop electrical supplies bonded together or separated?
 
  • Thread Starter Thread Starter
  • #8
If the flat and shop share water supplies then they could be bonded back to a common MET.

Are the flat and shop electrical supplies bonded together or separated?
The mains supplies are separate. The metered supply for the flat appears to be from the DNO see pic
 

pc1966

Arms
Esteemed
If the feed is getting fixed in SWA then no need to worry about the bonding as most likely it would be 16mm 3-core and fine for PME, then as you say a switch-fuse and sanity returns.

I presume you took the photo with the cover off the MCB/RCD and it is not normally like that!
 
  • Thread Starter Thread Starter
  • #10
If the feed is getting fixed in SWA then no need to worry about the bonding as most likely it would be 16mm 3-core and fine for PME, then as you say a switch-fuse and sanity returns.

I presume you took the photo with the cover off the MCB/RCD and it is not normally like that!
That’s the point - fixed with SWA is the ideal solution but would mean SWA clipped up the stairs and along a hallway or hacked into the plaster / I don’t really want the job to resolve it so may just give a C3 on the selectivity issue and leave it to them with some supporting notes. The bonding/main earth though is another issue which until I find the water supply can’t comment - currently a C2. And no I’ve removed the cover to do the Ze
 

SJD

-
Mentor
Arms
Esteemed
… fixed with SWA is the ideal solution but would mean SWA clipped up the stairs and along a hallway or hacked into the plaster ...
Is there a sensible route on the outside of the property, up/round an external wall instead?
 

Strima

-
Arms
Esteemed
Smart RCD at the supply end, expensive but saves walking down the stairs to reset it.
 
The 63A mcb is reverse fed. Is that correct? Need to check makers?

What size is the DNO's fuse? Can't the box with RCD and mcb be removed if DNO's fuse is 63A? Then direct from mainswitch isolator to remove CU using swa cable? Or does the main swa need additional protection as westward10 suggests?
 
Last edited:
  • Thread Starter Thread Starter
  • #18
The 63A mcb is reverse fed. Is that correct? Need to check makers?

What size is the DNO's fuse? Can't the box with RCD and mcb be removed if DNO's fuse is 63A? Then direct from mainswitch isolator to remove CU using swa cable? Or does the main swa need additional protection as westward10 suggests?
Yes as I stated earlier I think the RCD is wired upside down but operates correctly I assume once the double pole switch is closed it will function either way but whoever wired it made life difficult and the MCB doesn’t look designed to take 25mm csa. it’s a pig to get the cover back on too would fail the ip4x reg except it is not readily accessible but then thinking about it it is as the meter is designed to accessible to public.

DNO fuse is marked 60/80 not verified even at 60 the “tails” would then be about 10meters and the 6mm earth still an issue
 
Thx. I forgot about the tails having to be no more than 3m in length. So the 16mm main supply to the remote CU needs a protective break in it to be within the 3m. Hence a fuse, which will also solve the selectively between the mcb's at the remote CU and 63A mcb at the meter.

It appears best, as been suggested, to remove all, to have a fused switch, so all tripable protective devices are in one location inside the flat. The sub CU has two RCDs. So no going outside (lockable cupboard) to see what the problem is, or setset an RCD. Also the RCD has to be checked every six months by the user, so needs to be accessible.
 
Last edited:
  • Thread Starter Thread Starter
  • #21
Thx. I forgot about the tails having to be no more than 3m in length. So the 16mm main supply to the remote CU needs a protective break in it to be within the 3m. Hence a fuse, which will also solve the selectively between the mcb's at the remote CU and 63A mcb at the meter.

It appears best, as been suggested, to remove all, to have a fused switch, so all tripable protective devices are in one location inside the flat. The sub CU has two RCDs. So no going outside (lockable cupboard) to see what the problem is, or setset an RCD. Also the RCD has to be checked every six months by the user, so needs to be accessible.
But the problem remains of flouting the regulation requiring concealed cable protection by 30mA RCD ...
 
But the problem remains of flouting the regulation requiring concealed cable protection by 30mA RCD ...
It looks like earthing to gas and water pipes may not be a problem. To keep the existing 16mm sub main cable you need to have an RCD at the meter protecting it, as it is under plaster, removing the RCDs at the consumer unit. The flat would only have one RCD.

The cupboard would need a key which is also given to the resident, as they would need access to the meter and RCD to test it every six months and isolate the whole supply if needed. Even if a smart RCD is used, they still need access to fully isolate the supply.

I would assume some labelling stating what the equipment in the cupboard supplies (the flat, not the shop) and a clear label stating that the mainswitch isolates the flat.
Post automatically merged:

What is the ideal solution, with all the given suggestions?
 
Last edited:

pc1966

Arms
Esteemed
It sounds like a great idea, but only 40A rated so no use here, and hardly anyone seems to sell them. mostly eBay :(
 

Strima

-
Arms
Esteemed
It sounds like a great idea, but only 40A rated so no use here, and hardly anyone seems to sell them. mostly eBay :(
And most of the eBay ones have probably been nicked from BT... :D

I forgot to mention that their master and slave system is good. Master at source and the slave at the remote DB, only one will trip under fault conditions, so if your master trips it's the distribution circuit and if the slave trips it will be the final circuits.

Hopefully they will up their device ratings so this system could be more widely used in situations likes the OPs.
 
I forgot to mention that their master and slave system is good. Master at source and the slave at the remote DB, only one will trip under fault conditions, so if your master trips it's the distribution circuit and if the slave trips it will be the final circuits.

Hopefully they will up their device ratings so this system could be more widely used in situations likes the OPs.
As more outbuildings look to be used, the sooner the better.
As to this specific problem. One solution. Assuming the water pipe can be found and earth cable attached.
  • Keep the RCD and 63A mcb at the meter cupboard with the main isolator.
  • Use 16mm tails.
  • Tidy up the wiring.
  • Fit an SPD.
  • Connect the earth wires.
  • Remove the RCDs at the sub CU to eliminate selectivity problem with two RCDs in series.
  • Give user a key to cupboard.
  • Label the sub CU, and all inside the meter cupboard.
Post automatically merged:

It sounds like a great idea, but only 40A rated so no use here, and hardly anyone seems to sell them. mostly eBay :(
Also,
Earth grounding systems: TT and TN-S only
 
Last edited:
  • Thread Starter Thread Starter
  • #27
Submit the Report and worry about solutions if they are required by the client.
I’d like to be prepared with a solution !
 

pc1966

Arms
Esteemed
Seems the Schneider option would be suitable, such as:

It is wider, so that nasty enclosure and related stuff would need to be changed, and ideally a switch-fuse put in for over current and then the RED auto-recloser to avoid the need for cable replacement, so a bit of space juggling, but it would address the selectivity issue to a large degree (or at least some of the annoyance factor).
 