westward10 ~ Staff member Admin Esteemed Supporter Dec 21, 2023 #16 7029 dave said: Yes no RCD protection Click to expand... Submain is fine so needn't be included in the installation.
7029 dave said: Yes no RCD protection Click to expand... Submain is fine so needn't be included in the installation.
C cliffed ~ Arms Dec 23, 2023 #17 sub main looks like it will need Rcd protection, the other issue is the size of the cpc which will be ok if MBPC are not required at the Flat.
sub main looks like it will need Rcd protection, the other issue is the size of the cpc which will be ok if MBPC are not required at the Flat.
littlespark ~ Staff member Esteemed Arms Supporter Patron Dec 23, 2023 #18 The only reason it may need rcd protection is if it’s buried <50mm inside the other flats, and we don’t have that information. It’s no different than regular meter tails in terms of mechanical protection… it’s just a long length, which is taken care of by the 60A fuse.
The only reason it may need rcd protection is if it’s buried <50mm inside the other flats, and we don’t have that information. It’s no different than regular meter tails in terms of mechanical protection… it’s just a long length, which is taken care of by the 60A fuse.
DPG ~ Broke Internet Esteemed Arms Patron Dec 23, 2023 #19 OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface? I'm guessing not as you were talking about changing the cable or adding RCD protection.
OP - is this T&E run on the surface or in conduit all the way? Or is any of it below the surface? I'm guessing not as you were talking about changing the cable or adding RCD protection.