davesparks
The 63A mcb is reverse fed. Is that correct? Need to check makers?
MCBs, and most RCCBs, work either way round.
The 63A mcb is reverse fed. Is that correct? Need to check makers?
The 63A mcb is reverse fed. Is that correct? Need to check makers?
What size is the DNO's fuse? Can't the box with RCD and mcb be removed if DNO's fuse is 63A? Then direct from mainswitch isolator to remove CU using swa cable? Or does the main swa need additional protection as westward10 suggests?
Smart RCD | Eurocraft Tech - https://www.eurocraft.co.uk/product-page/smart-rcdWhat exactly do you mean by a smart RCD?
But the problem remains of flouting the regulation requiring concealed cable protection by 30mA RCD ...Thx. I forgot about the tails having to be no more than 3m in length. So the 16mm main supply to the remote CU needs a protective break in it to be within the 3m. Hence a fuse, which will also solve the selectively between the mcb's at the remote CU and 63A mcb at the meter.
It appears best, as been suggested, to remove all, to have a fused switch, so all tripable protective devices are in one location inside the flat. The sub CU has two RCDs. So no going outside (lockable cupboard) to see what the problem is, or setset an RCD. Also the RCD has to be checked every six months by the user, so needs to be accessible.
It looks like earthing to gas and water pipes may not be a problem. To keep the existing 16mm sub main cable you need to have an RCD at the meter protecting it, as it is under plaster, removing the RCDs at the consumer unit. The flat would only have one RCD.But the problem remains of flouting the regulation requiring concealed cable protection by 30mA RCD ...
It sounds like a great idea, but only 40A rated so no use here, and hardly anyone seems to sell them. mostly eBay

And most of the eBay ones have probably been nicked from BT...It sounds like a great idea, but only 40A rated so no use here, and hardly anyone seems to sell them. mostly eBay![]()

As more outbuildings look to be used, the sooner the better.I forgot to mention that their master and slave system is good. Master at source and the slave at the remote DB, only one will trip under fault conditions, so if your master trips it's the distribution circuit and if the slave trips it will be the final circuits.
Hopefully they will up their device ratings so this system could be more widely used in situations likes the OPs.
Also,It sounds like a great idea, but only 40A rated so no use here, and hardly anyone seems to sell them. mostly eBay![]()
I’d like to be prepared with a solution !Submit the Report and worry about solutions if they are required by the client.