The 63A mcb is reverse fed. Is that correct? Need to check makers?
What size is the DNO's fuse? Can't the box with RCD and mcb be removed if DNO's fuse is 63A? Then direct from mainswitch isolator to remove CU using swa cable? Or does the main swa need additional protection as westward10 suggests?
Yes as I stated earlier I think the RCD is wired upside down but operates correctly I assume once the double pole switch is closed it will function either way but whoever wired it made life difficult and the MCB doesn’t look designed to take 25mm csa. it’s a pig to get the cover back on too would fail the ip4x reg except it is not readily accessible but then thinking about it it is as the meter is designed to accessible to public.
DNO fuse is marked 60/80 not verified even at 60 the “tails” would then be about 10meters and the 6mm earth still an issue
Thx. I forgot about the tails having to be no more than 3m in length. So the 16mm main supply to the remote CU needs a protective break in it to be within the 3m. Hence a fuse, which will also solve the selectively between the mcb's at the remote CU and 63A mcb at the meter.
It appears best, as been suggested, to remove all, to have a fused switch, so all tripable protective devices are in one location inside the flat. The sub CU has two RCDs. So no going outside (lockable cupboard) to see what the problem is, or setset an RCD. Also the RCD has to be checked every six months by the user, so needs to be accessible.
But the problem remains of flouting the regulation requiring concealed cable protection by 30mA RCD ...
It looks like earthing to gas and water pipes may not be a problem. To keep the existing 16mm sub main cable you need to have an RCD at the meter protecting it, as it is under plaster, removing the RCDs at the consumer unit. The flat would only have one RCD.
The cupboard would need a key which is also given to the resident, as they would need access to the meter and RCD to test it every six months and isolate the whole supply if needed. Even if a smart RCD is used, they still need access to fully isolate the supply.
I would assume some labelling stating what the equipment in the cupboard supplies (the flat, not the shop) and a clear label stating that the mainswitch isolates the flat.
[automerge]1591356214[/automerge]
What is the ideal solution, with all the given suggestions?
It sounds like a great idea, but only 40A rated so no use here, and hardly anyone seems to sell them. mostly eBay :(
And most of the eBay ones have probably been nicked from BT... :D
I forgot to mention that their master and slave system is good. Master at source and the slave at the remote DB, only one will trip under fault conditions, so if your master trips it's the distribution circuit and if the slave trips it will be the final circuits.
Hopefully they will up their device ratings so this system could be more widely used in situations likes the OPs.
As more outbuildings look to be used, the sooner the better.
As to this specific problem. One solution. Assuming the water pipe can be found and earth cable attached.
  • Keep the RCD and 63A mcb at the meter cupboard with the main isolator.
  • Use 16mm tails.
  • Tidy up the wiring.
  • Fit an SPD.
  • Connect the earth wires.
  • Remove the RCDs at the sub CU to eliminate selectivity problem with two RCDs in series.
  • Give user a key to cupboard.
  • Label the sub CU, and all inside the meter cupboard.
[automerge]1591364876[/automerge]
Also,
Earth grounding systems: TT and TN-S only
This in my eyes would be a C3 issue and most clients often don't want C3 issues to be overcome.
Seems the Schneider option would be suitable, such as:
It is wider, so that nasty enclosure and related stuff would need to be changed, and ideally a switch-fuse put in for over current and then the RED auto-recloser to avoid the need for cable replacement, so a bit of space juggling, but it would address the selectivity issue to a large degree (or at least some of the annoyance factor).
Mark.fardon,
John-SJW,