This vid by John Ward focuses on the
impedance. Combined with the first vid I posted by him, the size of the
earth conductor can be calculated. It seems 0.3 ohms will be OK or the calc, but needs checking. his vid helps and does the calc.
If the earth is fine below 6mm then the T&E can remain. If not, it needs replacing. To save expense and hassle by keeping the T&E, if the 6mm earth size is fine, then use a 63A mcb and Smart RCD at the meter location. Then remove the RCDs in the CU. Bond the main earth terminal to the gas pipe, then if possible bond the CU to the water pipe.
The only caveat is that if a 10mm earth cable is run to the water pipe on the far side of the house, from the CU, the undersized 6mm conductor in the 16mm T&E may be suitable meaning the T&E can remain. I am not up on that. Others may help.
View: https://www.youtube.com/watch?v=HsWWKzjVUxE
[automerge]1591621490[/automerge]
I just looked at John Ward's vids. By the figures he has used (typical figures) for the
earth cable size, It looks like the 6mm earth conductor in the T&E is fine. The calcs give the
correct size. The read off ballpark table says just keep the earth conductor size the same as the tails - they obviously side on caution in read off ballpark tables keeping the conductor size large, in case.
I changed some of the parameters here and there to represent changes in some systems, and always it came in under 6mm