davesparks
Seems the Schneider option would be suitable, such as:
18685 - RCCB with re-closer - RED - 2 poles - 63 A - class A - 30 mA | Schneider Electric India
Schneider Electric India. 18685 - RCCB with re-closer - RED - 2 poles - 63 A - class A - 30 mA.www.se.com
It is wider, so that nasty enclosure and related stuff would need to be changed, and ideally a switch-fuse put in for over current and then the RED auto-recloser to avoid the need for cable replacement, so a bit of space juggling, but it would address the selectivity issue to a large degree (or at least some of the annoyance factor).
In my opinion that still would not comply, it will not minimise disruption in the event of a fault.
Yes it will auto re-close in the event of a nuisance trip, but that doesn't avoid nuisance tripping in the first place, or leave any circuits live during a genuine fault.