Discuss Sequence of tests in guidance note 3 (initial verification) in the UK Electrical Forum area at ElectriciansForums.net

then Ze at board and add to your R1+R2 at furthest point or highest reading etc to get you Zs to make sure ADS can be archived.

of-course you can do direct direct Zs measures at the end of the circuit.

Ze should be at the suppliers terminals where the consumers tails connect.
The loop impedance tested at a DB is a Zs, it is only in small installations, such as domestic, that you might be taking a Ze measurement at the CU as it may be the first available point to connect test leads.

Calculating Zs is a poor alternative to measurement and should, in my opinion, always be measured.
 
Do you do tutorials? :cool:
Do I do tutorials? I'm a commercial installer, certainly not a tester, no one would allow me, not without supervision, so I gather experience where I can. Also, as you can imagine different testers have different ways of doing things so I have to keep to common sense and theory/facts, not to opinions. A lot of things actually tested poorly, again due to time constraints, and maybe laziness, sometimes dbs are energised even before dead testing them, for example so that other trades could test their gear etc. not unheard of.
 
I guess I'm thinking commercial sites, where you get Ze of Ze of Ze so only the main is true Ze, the rest are Zs at Db is it not? If you were given Ze by the DNO and measured Ze at DB, and they would differ, would that mean the board is sub main? But in any case which of the two "Ze" would you choose to calculate the Zs of final circuits?

Ze is, and can only be, the loop impedance of the external supply.
Ze is, strictly, measured at the point where the consumers equipment connects to the suppliers equipment with the consumers equipment disconnected (except the earthing conductor which can remain connected to the suppliers equipment but disconnected from the installation) . But often, especially in domestic and small installations, the first available point to connect the test leads is the CU or DB which then leads to confusion for some people.

However the tests for Ze and Zs at the DB are still different, Zs at the DB, and PEFC, is done with earthing conductor connected to the consumers installation which can, and often does, affect the value measured.

Just to confuse things further a properly measured Ze will usually be different to that quoted by the DNO as they will normally quote their maximum design limit rather than a value specific to your supply. So for a 100A SPN TNCS supply they will usually quote a Ze of 0.35 and PFC 16kA (which isn't possible if you think about it)
[automerge]1596738147[/automerge]
sometimes dbs are energised even before dead testing them, for example so that other trades could test their gear etc. not unheard of.

That was normal practice years ago, give it a quick test on the megger and switch it on, maybe not even bothering with the megger.

Even when I was training testing was treated as a nuisance to be done at the end of the job, long after the installation was energised.

I'm sure we've all seen DBs with big ---- stains in them where someone obviously switched the supply on without any testing.
 
I could never understand the 'enquiry' route. It's quite obvious that the maximum allowed will be given...how could the authority know the true value. The only point is the fact that, on their records at least, it's possible to deduce whether it's listed as a TNS or TNCS system, without inspection.
 
I could never understand the 'enquiry' route. It's quite obvious that the maximum allowed will be given...how could the authority know the true value. The only point is the fact that, on their records at least, it's possible to deduce whether it's a TNS or TNCS system, without inspection.

The enquiry route becomes more useful at the design stage and with bigger supplies. I think we all know what the by enquiry value is for standard 100A TNS, TNCS and TT. For big supplies they will give stated figures on a case by case basis.
For design work you can usually only go by the stated figures as the supply isn't there yet to measure it.
[automerge]1596739449[/automerge]
Now I'm confused.

Ze is the loop impedance of the external supply, it is measured with the earthing conductor disconnected so that no parallel paths from the installation are included in the test.
Zs is measured with the earthing conductor connected so that all parallel paths in the installation are included in the test.

So for a small installation with only one CU you could measure Ze at the main switch terminals and the disconnected earthing conductor and get 0.35, then reconnect the earthing conductor and measure Zs from the same place and get 0.33.
The difference being the parallel paths due to the various protective conductors connected.
This is why the PEFC is taken with the earthing conductor connected, the value may be higher this way.
 
Last edited:
The enquiry route becomes more useful at the design stage and with bigger supplies. I think we all know what the by enquiry value is for standard 100A TNS, TNCS and TT. For big supplies they will give stated figures on a case by case basis.
For design work you can usually only go by the stated figures as the supply isn't there yet to measure it.
You're preaching to the converted, mate. I've been dealing with supply authorities regarding commercial and industrial premises, old and new, for decades.
 
Zs is measured with the earthing conductor connected so that all parallel paths in the installation are included in the test.
Oh I think I got you confused, I meant Ze. Ze which you test with the earthing conductor disconnected(due to parallel paths). On the test results sheet you put that value under Zs at DB because it can be either main or submain board in which case not true Ze. That's how I understand it.
 
Oh I think I got you confused, I meant Ze. Ze which you test with the earthing conductor disconnected(due to parallel paths). On the test results sheet you put that value under Zs at DB because it can be either main or submain board in which case not true Ze. That's how I understand it.
On the 'other' additional, sheets there won't be a position for Ze, it'll ask for Zs.
 

Reply to Sequence of tests in guidance note 3 (initial verification) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
822
Because none of us are beyond schoolboy errors.......... Doing some events kit testing over the weekend, some larger metal stand distro panels...
Replies
7
Views
1K
Hi this is my first post, I’m looking for some advice I’m doing my Inital verification course as part of my NVQ. I’ve passed the practical part...
Replies
2
Views
1K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
621
Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock