I use tape on large lugs, always have done and I thought your taping job was very neat. If the tape unwraps then it's either cheap rubbish tape or it wasn't put on properly.
 
Pity you didn’t put the lugs on the opposite way around. They align better between the gland plate and terminal.

TermBox6_zps73ced673.jpg


We usually used 600mm 4 sector solidal. Brass glands and locknuts though a slotted steel gland plate, the slots filled with epoxy.

Gland-plate_zps243007ab.jpg
 
Jesus wept, AWA glands come with Ali lock nuts and Ali banjo's.... RoB2 obviously hasn't used them before....

Why in the name of god would you use banjos on a metal gland plate?

What purpose would they serve?

The transformer glands are quite adequately earth via the aluminium plate so no need for banjos, the switchgear end is in to an insulated gland plate. Having an earth at both ends would cause circulating currents.

I await your answer with interest.
 

Reply to Sexual - Still makes me tingle in the UK Electrical Forum area at ElectriciansForums.net